Discuss Temporary supply to portacabins in the The Welcome Forum area at ElectriciansForums.net

Reaction score
277
I have three portacabins arriving on site.
Each cabin is pre-wired and has a 32A plug connected to the consumer unit.
They are 80m from the site distribution board.
I need some suggestions on the best and cheapest way to feed these.
The option I've come up with is run 3 lengths of 3 core swa and simply put a 32a connector on the end of each. This would involve me running 3 lots of 6mm cable and placing a 32a rcbo for each circuit at the dis board.
I was also considering running a single cable to the first portacabin and then distributing to each of the CU from here, but the cable would need to be 25mm swa, given I need about 30a at each cabin ( not continuously).
 
how many circuits in each cabin? and what's the fabric of the cabin. wood or steel?
 
The cabins are wooden, two circuits in each.
6A lighting in each and a 32A ring in each.
All 230v.
Cabin one is a changing and drying room with a 3kva heater . Cabin 2 is welfare, a couple of 13a sockets for a kettle and radio.
Cabin 3, is the site office, usual heater and lap tops
 
why not run out a 3 phase cable, split at first cabin 1 phase for each. and with only 2 circuits per cabin, division of circuits does not apply, so a RCD main switch in each CU would be cheaper than RCBOs. i should think this is already in situ, using a standard 2 circuit "garage board".
 
I was thinking doing this, but it would mean splitting the phases down in an IP44 board outside the cabins, as we can not drill into the cabins as part of the hire agreement.
I'd probably need to run a 5 core 10mm swa from the distribution point and the mount a board on the adjacent wall. Then break each phase from here.
Do you have a board you would recommend. I've used giwiss in the past, but these can work out expensive for a project only lasting 6 months
 
Materials cost what they cost, you can't do a rubbish job because it costs money to do it properly. I'm almost certain the board inside the cabins will have rcd protection on them. I wouldn't bother putting rcd protection on the supply armoureds.

Either run each supply separately using the correctly sized swa probably 6mm from the dis board

Or use Tels idea of running a 3 phase cable and teeing of per each cabin. Mount a gewiss on top of the cabin and secure with zip ties through the tie eyes on the cabin.

Or run a supply to an external meter box nearer the cabins using a larger cable and distribute From there.
 
Cheers lankywill.
I never had any intention of doing a "rubbish" job. I wanted to do the most cost affective.
There is more than one way to skin a cat. I just wanted the cheapest way to do it safely, given its only for 6 months.
 
I'm not trying to come across offensive mate, I know what it's like when the boss wants everything done for squat. That said the cheapest is probably 3 separate armoureds by the time you add all the gewiss boxes and glands. I'd get some cable quotes and go from there, eddies usually do armoured pretty cheap
 
No offence taken :).
You are correct, the boss wants it cheap as chips. I jokingly said a choch block, poly bag and insulation tape would do it. He thought I was being serious.
Cost wise...3 separate cables, but it will take me longer banging in 300+ cleats.
Nite all.
Glad I joined the forum, been reading it for a few years now.
You all seem a friendly bunch of sarky sparkles.
 
how many circuits in each cabin? and what's the fabric of the cabin. wood or steel?
Cabin usually steel , circuit no's 1* LGt 1* ring 2* htg or air con
Majority of power used is heating or cooling 4 kw max , power usually very minimal , couple of pc's and phone chargers
Offices don't take much load it's the canteens , drying rooms and toilets you have to consider loads more
 

Reply to Temporary supply to portacabins in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
553
A friend of mine wired a 10mm 3 core armoured cable to his shed before I got involved and wired it himself already. He wants make it an air bnb...
Replies
8
Views
879

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock