Discuss Testing a PV system. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

P

pburley

Hi guys

Just had a call from a friend who's brother as fitted a 4Kw system to his roof. He would like me to test it. I've not done any work on PV systems and not sure what tests need to be done. I first thought an installation cert should be done but after reading bit on this site im not so sure. I hold a C+G 2391 cert is this enough?

Many thanks guys.
 
Secondly, To benefit from the feed in tariff you will need to complete all relevant MCS paperwork & all equipment needs to be MCS certified. Is your business registered MCS?
 
ac circuit, test as usual.

DC, test open circuit voltage & amps, then compare with the data sheets and expected values bearing in mind the light levels and temperatures of the panels - note, most MF testers for AC testing don't do DC, or ampage, either get a specialist bit of kit or multimeter that can take the anticipated DC voltage and ampage.

also test DC continuity and insulation resistance, though tbh most solar inverters already do this on start up, so if there were a problem then the inverter would have picked it up.

The main way that noobs are likely to cock up the DC citcuit IME is by not making the connectors properly either by not crimping properly, or by not tightening up the seals so that water can run into the connectors, neither of which is picked up by any testing, so a visual inspection of this wouldn't be a bad idea, or at least ask him about it - they mostly need spanners / grips to tighten properly onto 4mm2, or 2.5mm2 cable, so if he only hand tightened, there's a good chance it's not water tight unless he's got a particularly fierce grip.
 
One of the Suby teams installing panels, have not been carrying out the pre VOC/ISC checks before fitting on the roof. Is this mandatory test or just a good idea if there is a fault with the panel post install.

.
 

Reply to Testing a PV system. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi again. Following my recent zero-Riso issue (unresolved) and also because my system has, in any case, been prone for a good while to the odd...
Replies
10
Views
1K
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
952
I was thinking about getting qualified to do this for a charity. I already do the necessary stuff to put the electrical donations into the shop...
Replies
0
Views
702
Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K
I am never quite sure if I am doing too little or too much when someone has a flood and I am called in. The most recent example is a chap has had...
Replies
4
Views
826

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock