sparkymatt1987

Hi If I were to spur off a ring main to a fcu that will feed an outside light. What would be the test procedure I would carry out. Obviously a continuity of ring would not test upto the light so how would this be done
 
your r1 + r2 ( end/end) would not be affected by the addition. you would get a very small increase in your R1+R2 at the FCU ( depending on the length of the cable between the socket and FCU). the cable from the FCU to the light is irrelevant as it's not part of the fixed wiring. you take you readings at the FCU ( including Zs)
 

Reply to Testing a spur in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
670
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
672
Hi. Has anyone ever taking a feed from an outside light to use as a spur to fit an outside plug to plug in a plug in ring camera. The only feed...
Replies
2
Views
205
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Im running a ring main for all my sockets using 2.5 cable....as an after thought i was thinking to spur off one of my socket outlets and run up...
Replies
4
Views
557

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock