CBR units appear difficult to trip time test on some occasions. Not only myself but other colleagues too when testing 300ma/500ma CBR units find even using a variety of manufacturers instruments that multiple trys are required before a succesful trip test. Often no trip occurs at all. Is this impedence related. ie TT systems.
 
I'm not good with acronyms so you'll have to remind me what a CBR actually is.
I know it's one of the permutations of an RCD, my guess would be its an earth leakage relay operating a circuit breaker via a shunt or release
 
Is it vigi type units which fail or seperate earth leakage relays with core balance transformers?

Core balance transformers need to be correctly installed to work properly, including getting the conductors centred in the coil, not off to one side etc.
 
Is it vigi type units which fail or seperate earth leakage relays with core balance transformers?

Core balance transformers need to be correctly installed to work properly, including getting the conductors centred in the coil, not off to one side etc.
Seperate controls. You know the type. 3 "inch square panel small rotary knobs for time delay and Current setting. Core installation complete in all cases. This issue is just occasional but given we install dozens annually the test failure rate though small is significant. It's a mystery though an Engineer from Kewtech did suggest that rcd testers specific to CBR units were available.
 
Seperate controls. You know the type. 3 "inch square panel small rotary knobs for time delay and Current setting. Core installation complete in all cases. This issue is just occasional but given we install dozens annually the test failure rate though small is significant. It's a mystery though an Engineer from Kewtech did suggest that rcd testers specific to CBR units were available.

I know the type very well, I've installed a fair few in various bits of equipment.
I've never yet had an issue testing them, I usually test them at 30mA and a randomly selected higher setting.

At the moment I can't think why they would not pass testing with a normal tester.
 
I know the type very well, I've installed a fair few in various bits of equipment.
I've never yet had an issue testing them, I usually test them at 30mA and a randomly selected higher setting.

At the moment I can't think why they would not pass testing with a normal tester.
Thanks Dave.
If we ever discover the answer I will be sure to let you know.
 

Reply to Testing CBR units in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
570
A friend of mine asked me to look at here PV system as she is not getting any power (and thus money) from it. First real issue is the Aurora...
Replies
8
Views
5K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Having a bit of a mare at the moment with a small 2 story HMO (6 single rooms with shared kitchen) which was fitted relatively recently (2016 or...
Replies
18
Views
2K
BACKGROUND I live in a small town where it is difficult to find ceritified electricians. In fact, electrician certification is not common for...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock