Discuss Testing extraneous conductive part in the UK Electrical Forum area at ElectriciansForums.net

But what is the use of testing between 2 points if they are connected together somewhere in the installation?
Like for instance a gas pipe and a known earth, but the gas pipe is connected at one end to the boiler which is connected to earth by a cpc. The cpc needs disconnecting at the boiler end then test between earth and the pipe.
That’s just one example you do not necessarily have that scenario every time of having to disconnecting anything.
 
Last edited:
Thats the idea of this test; to discover if somehow two points are connected in someway or not.
Extract taken from NAPITS site guide, the point is actually to find out if the metallic conductive part is introducing an earth potential into the installation and by testing between the earth of the installation and the conductive part, that the conductive part under test has a high enough resistance to earth that it doesn’t require bonding to the earthing arrangement of the installation
FA78B2F7-1ECF-472D-A970-6C454CB8E621.jpeg
9320013B-3705-4C2E-B211-39E77FE3E23C.jpeg
It’s
 
Last edited:
Extract taken from NAPITS site guide, the point is actually to find out if the metallic conductive part is introducing an earth potential into the installation and by testing between the earth of the installation and the conductive part, that the conductive part under test has a high enough resistance to earth that it doesn’t require bonding to the earthing arrangement of the installation

Fair enough. But that’s just one piece of guidance that says dis the cpc’s, against the two I posted, which suggested using cpc’s as the known earth.

Does Guidance Note 3 or 8 make any suggestions?
 
Fair enough. But that’s just one piece of guidance that says dis the cpc’s, against the two I posted, which suggested using cpc’s as the known earth.

Does Guidance Note 3 or 8 make any suggestions?
It’s only relevant to disconnect the cpc’s if required, you don’t always need to if the metallic part has not been connected together with a cpc to earth .
I don’t think gn3 covers this subject but gn5 and 8 do so I’ll have a dig out
 
It says in GN8 to test between the MET and the suspected extraneous conductive part.

Not a problem in a domestic installation but a known/proven connection to earth is more practical in a commercial/industrial scenario.
 

Attachments

  • Extraneous conductive parts.pdf
    4 MB · Views: 17
So, I carried out this test yesterday on some cable basket I put up for some Cat6 data cables. I tested between a known earth from a socket outlet and the cable basket and I got a reading of 0.47 ohms. Nice low reading via parallel paths (earthed structural metal work). I then bonded the basket using some 6mm.

So am I right in thinking that this needed bonding due to the reading, and if the reading had been above 23,000 ohms then it wouldn't have needed bonding?
 
I don't think it needed bonding. Here's a view from someone else;

 
If any current was entering that exotic French link then the Disconjoncteur tetrapolair de branchement would trip, can't see how any current could enter the TT earthing system without tripping something, perhaps even the Parafonudre Disconjoncteur Quata would go first.
 
There are safety procedures that we all go through before we carry out any work on a system, why are you persevering with this premise?
 

Reply to Testing extraneous conductive part in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
635
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
663
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
758

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock