Can you not test at the nearest place which can be accessed without shutting down and note this on the cert.....if that is a DB close or connected at the origin the difference will be neglegable.
 
Can you not test at the nearest place which can be accessed without shutting down and note this on the cert.....if that is a DB close or connected at the origin the difference will be neglegable.
I thought that the Ze on a circuit could only be measured at where the suppliers incomer ends and the consumers equipment starts
 
It can be obtained by enquiry or measurement.

Sometimes ze cannot be measured as bonding conductors can't be removed etc. If I'm ever in this position iwill record the enquiry reading, and then measure a couple of local zs readings if possible just to assure myself.
 
It can be obtained by enquiry or measurement.

Sometimes ze cannot be measured as bonding conductors can't be removed etc. If I'm ever in this position iwill record the enquiry reading, and then measure a couple of local zs readings if possible just to assure myself.
There is only one Ze in an installation is that right, every thing after that is Zs
 
would that be acceptable,what if the earth was not as good as it should be

Your line / earth impedance reading can only be lower testing it at any other point than origin due to the parallel paths of the main bonding.

I thought that the Ze on a circuit could only be measured at where the suppliers incomer ends and the consumers equipment starts

Correct Ze can only be measured at origin.

As a limitation though test at closest accessible point to origin with bonding still connected and note this figure as Zdb.
 
Your line / earth impedance reading can only be lower testing it at any other point than origin due to the parallel paths of the main bonding.



Correct Ze can only be measured at origin.

As a limitation though test at closest accessible point to origin with bonding still connected and note this figure as Zdb.
Thanks m8, after all the reading I've done on testing I've never came across that one, I'd just like to be sure if my boss put me over it.
By the way Im from Newry, I noticed that your from Belfast.
 
There is only one Ze in an installation is that right, every thing after that is Zs

Correct


I said I then measure ZS at other points. Typically because if you have a circuit with an R1&R2 of say.. O.24, and you measure a zs of 0.84 on a TNC-S system then you would suspect the Ze to bearound the 0.6 area.. Which exceeds the maximum.



Ze measured downstream from the origin is considered Zdb, only measured downstream on the supply side of consumer units though.
 
Last edited:
Correct


I said I then measure ZS at other points. Typically because if you have a circuit with an R1&R2 of say.. O.24, and you measure a zs of 0.84 on a TNC-S system then you would suspect the Ze to bearound the 0.6 area.. Which exceeds the maximum.



Ze measured downstream from the origin is considered Zdb, only measured downstream on the supply side of consumer units though.
How is that calculated, or is there an equation for that
 
Thanks m8, after all the reading I've done on testing I've never came across that one, I'd just like to be sure if my boss put me over it.
By the way Im from Newry, I noticed that your from Belfast.

Another one from Norn Iron then think there are a few more on here.
 
Alright guys, I have just been at a house to fit a 32amp pull cord, when I went to the consumer unit there was a 16mm earth coming from a cut out that was fed with just two tails ,this is a TT system ,so I did a Ze and got a reading of 1.34ohms ,what kind of readings should I be getting? I think I am going to have to drive a spike.:eek:
 
Alright guys, I have just been at a house to fit a 32amp pull cord, when I went to the consumer unit there was a 16mm earth coming from a cut out that was fed with just two tails ,this is a TT system ,so I did a Ze and got a reading of 1.34ohms ,what kind of readings should I be getting? I think I am going to have to drive a spike.:eek:


I'd say 1.34 ohms was pretty good for a TT system :D
 
Alright guys, I have just been at a house to fit a 32amp pull cord, when I went to the consumer unit there was a 16mm earth coming from a cut out that was fed with just two tails ,this is a TT system ,so I did a Ze and got a reading of 1.34ohms ,what kind of readings should I be getting? I think I am going to have to drive a spike.:eek:

The 16mm earth coming from the cut out is strange for a TT
 
The 16mm earth coming from the cut out is strange for a TT
I dont think it is doing any thing some one has just connected it in there for the sake of it so what do you think is that a decent enough reading ,if so must be getting an earth from some where that is not visible :confused:
 

Reply to Testing limitations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
864
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I'm fitting one of the Apex 7S units on Friday. I'd avoided the original range after a couple of bad experiences but I figured a new model might...
Replies
6
Views
762
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
447
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock