Hi Again Guys,

I've just wired a garage unit and have fed It from a 32A MCB from the main cu in the house, so its a new circuit. I have tested the new unit and all is fine. The question I have is.. Do I have to test all circuits in the original cu as well and record results on the same test schedule as the garage one?

There are no records/certs/charts for the original cu.

Thank you all in advance
 
You are only responsible for the new circuit that you have installed.
You will need to record other details from the CU like ZE PFC and make sure the bonding is up to date if required!
 
You just need to test and record the new circuit you have put in Bob, and then complete an EICR.

Also, because you have created a new circuit the work will be notifiable, so this may be a good job to show your assesser if you are not already part of a scheme.

Also you would need to make sure the Main earthing and Main bonding are acceptable.

........

I think we all typed at the same time!!
 
One tip for you when filling out the EIC for the "existing" CU, where the CU has existing circuits put "used" against these circuits, fill out the full details for your new circuit, and use "spare" for any remaining circuits.

Then on the sheet for your new CU in the garage fill out the cert for your new circuits, then "spare" for any unused.

Hope this helps.
 
One tip for you when filling out the EIC for the "existing" CU, where the CU has existing circuits put "used" against these circuits, fill out the full details for your new circuit, and use "spare" for any remaining circuits.

Then on the sheet for your new CU in the garage fill out the cert for your new circuits, then "spare" for any unused.

Hope this helps.


the old cu has no ID on any of the circuits so I can just write used where circuit description is? other wise I need spend some time finding out whats what. the old unit was fitted by the kitchen fitter. it has one rcd protecting 2x 32a circuits and all other circuits unprotected. its a chint board
 
the old cu has no ID on any of the circuits so I can just write used where circuit description is? other wise I need spend some time finding out whats what. the old unit was fitted by the kitchen fitter. it has one rcd protecting 2x 32a circuits and all other circuits unprotected. its a chint board

Yes.

As for the Chint - is that a spelling mistake as I think they are shint!
 
One tip for you when filling out the EIC for the "existing" CU, where the CU has existing circuits put "used" against these circuits, fill out the full details for your new circuit, and use "spare" for any remaining circuits.

Then on the sheet for your new CU in the garage fill out the cert for your new circuits, then "spare" for any unused.

Hope this helps.

What if you regularly add odd circuits to large DB's, say, 16way, 3 phase. Don't think I'd be doing circuit details and test results with fifty 'used' and 'spare' lines...:biggrin:
 
What if you regularly add odd circuits to large DB's, say, 16way, 3 phase. Don't think I'd be doing circuit details and test results with fifty 'used' and 'spare' lines...:biggrin:

Most of is doing that kind of thing use software to fill in certs, so you can just fill in your new circuit details then fill in one of the others a used and copy that to all the blanks.
 
Most of is doing that kind of thing use software to fill in certs, so you can just fill in your new circuit details then fill in one of the others a used and copy that to all the blanks.

Precisely.

Select "all results" when copying, remove previous line(s), add new details, job done.
 

Reply to testing new and old db in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
848
Hi All I have been asked to supply a minor works certificate on a smart thermostat upgrade. Would I just test the dedicated circuit from the CU...
Replies
3
Views
297
Just a quickie the new amendment certs now have tick boxes for the SPD… would you still add it to the schedule list for the DB… ie: At the top of...
Replies
2
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, I am in the process of training to be an electrician and have a question. When filling out a EIC for a new circuit am I required to test...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock