Discuss testing novice in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Dalf

-
Reaction score
10
Hi guys just after some help. I have not done alot of testing so I apologise if this is a stupid question.

Ring main. Getting end to ends all ok. Breaker stays on but as soon as my tester is plugged in to get zs or an appliance is plugged in it trips the rcd. Also when tester is plugged in it says connect error.

What is usually the most common fault for this?

Thanks
 
What tester are you using, some robins, you have to bypass the rcd to get a zs, what other tests have you done, what about ir? Is it any appliance or one thing in particular, lots of variables to answer first I'm afraid
 
No. I have not barely done any testing as I work for a big company who have just testers.but had to go to a job which is ending an the lad who wired it is on holiday, it was supposably tested but they plugged in fridge. Trips rcd straight away. So tried something different an exact same thing
 
Check neutral tails from the RCD's to the individual bars are in the right bars and not crossed, that's caused me a headache before
 
All sockets where checked and they looked fine but then ran out of time so back in tues for further investigation. Did try another rcbo an still the same.
 
If you tried another RCBO and the circuit passed an IR test then my money is on a neutral fault, crossed, borrowed or otherwise incorrectly wired.
 
I would dead test the cct and test every point with the figure of 8 method (again) IMO something has been connected up incorrectly. I don't use a 1700 series Megger but surely the tester is pointing to a connection issue and plugging something in the RCD is seeing the fault!
 

Reply to testing novice in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
561
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
896

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock