Discuss Testing questions? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Colin33

-
Arms
Reaction score
69
I haven't done any testing for a long time so some help with a few questions muchly appreciated please!

Firstly, earthing. The supply cable (from underground) appears to have several strands of the sheathing coated in black insulation and which is used as the neutral with the remaining bare sheathing as earthing. I've not seen this before, only the usual TNCS where the whole of the sheathing is the combined earth/neutral. Does this mean I have a TNS system? BTW, the Ze measurement is 0.16

Secondly, this is an all RCBO installation. However, when testing the trip times of all circuits generally come up with the same reading of 19ms, even on the fast trip test. There were a few minor variations when switching test between 0 & 180 degrees but 19ms was the favourite reading! I'm presuming that these particular rcbo's won't trip any faster than this?

Also, all circuits have a combined fixing method in that parts of the wiring are clipped direct to timber above the loft insulation, then drop into conduit in plastered walls and/or through insulated stud walls, and sometimes into plastic trunking and conduit in places. Which 'reference method' should one choose to put on the paperwork in this instance?

Cheers....
 
I haven't done any testing for a long time so some help with a few questions muchly appreciated please!

Firstly, earthing. The supply cable (from underground) appears to have several strands of the sheathing coated in black insulation and which is used as the neutral with the remaining bare sheathing as earthing. I've not seen this before, only the usual TNCS where the whole of the sheathing is the combined earth/neutral. Does this mean I have a TNS system? BTW, the Ze measurement is 0.16

Secondly, this is an all RCBO installation. However, when testing the trip times of all circuits generally come up with the same reading of 19ms, even on the fast trip test. There were a few minor variations when switching test between 0 & 180 degrees but 19ms was the favourite reading! I'm presuming that these particular rcbo's won't trip any faster than this?

Also, all circuits have a combined fixing method in that parts of the wiring are clipped direct to timber above the loft insulation, then drop into conduit in plastered walls and/or through insulated stud walls, and sometimes into plastic trunking and conduit in places. Which 'reference method' should one choose to put on the paperwork in this instance?

Cheers....

1 The cable is concentric and the earthing system is usually TN-C-S (concentric is used on TN-C-S supplies to lessen the chance of broken PEN conductors)

2 It's unusual to have such consistent tripping times but assuming confidence in your test instrument, that's what it's reading.

3 Record the worst-case reference method then you're always covered!
 
1 The cable is concentric and the earthing system is usually TN-C-S (concentric is used on TN-C-S supplies to lessen the chance of broken PEN conductors)

2 It's unusual to have such consistent tripping times but assuming confidence in your test instrument, that's what it's reading.

3 Record the worst-case reference method then you're always covered!


TNCS systems I've seen before have not had a few strands of the sheath with black insulation, that's what's confusing me. Also, there is usually a PME warning sticker put in place by the DNO but there isn't one in this case?

If I record the worst-case reference method then wouldn't questions be asked as to why I haven't applied the relevant correction factors to the circuits?
 
2 It's unusual to have such consistent tripping times but assuming confidence in your test instrument, that's what it's reading.

And 19mS is bloody fast, have a look at the requirements of 415.1.1

Cheers............Howard
 
2 It's unusual to have such consistent tripping times but assuming confidence in your test instrument, that's what it's reading.

And 19mS is bloody fast, have a look at the requirements of 415.1.1

Cheers............Howard

Yes it's well within requirements, but usually get around 12ms with the regular rcd's (as opposed to these rcbo's)
 
Firstly, earthing. The supply cable (from underground) appears to have several strands of the sheathing coated in black insulation and which is used as the neutral with the remaining bare sheathing as earthing.

This is the modern DNO cable for TN-S, it's called a ''Split Concentric cable''. It is basically the same as the TNC-S/PME concentric cable, but has, as you have stated, insulated neutral conductors (strands) and bare earthing conductors strands forming the concentric sections.
 
This is the modern DNO cable for TN-S, it's called a ''Split Concentric cable''. It is basically the same as the TNC-S/PME concentric cable, but has, as you have stated, insulated neutral conductors (strands) and bare earthing conductors strands forming the concentric sections.

Ah, thanks for that. So it is a TNS supply rather than a TNCS then? The Ze seems rather good for a TNS supply though??
 

Reply to Testing questions? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
676
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
612
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi Everyone, Sorry for all the questions. With he help of a friend, I recently installed some insulation into my mother's loft. Whilst adding...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock