Discuss Testing Rcd in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
No.........
Great forum this not been on for a while this was raised in a conversation the other day with someone and there argument was why is there a check box next to each circuit so I'm right in thinking you just put 1 and 5 times results in once and although not necessary the socket test would suffice
Great forum this not been on for a while this was raised in a conversation the other day with someone and there argument was why is there a check box next to each circuit so I'm right in thinking you just put 1 and 5 times results in once and although not necessary the socket test would suffice
The "danger" with doing that is that could be interpreted that only a single circuit is covered by the RCD.
I've done a CU change today - 10 way board, 4 circuits one side, 3 the other - I test each RCD and enter the results for the circuits "covered" for each.
If you were adding a new circuit, then results for the single circuit would be in order.
I guess it depends on the scope of the work you've been doing!
Just saying.
they have them because they could be fed by rcbo'sGreat forum this not been on for a while this was raised in a conversation the other day with someone and there argument was why is there a check box next to each circuit so I'm right in thinking you just put 1 and 5 times results in once and although not necessary the socket test would suffice
Eaton RCBO Pod being a good example of test anywhere BUT at the terminals... lolJust the one full procedure for each RCD....AT THE RCD TERMINALS!! Those check boxes come in very handy for RCBO's, otherwise just use the same values gained for each circuit.
Socket RCD testing can give you false mA values, remember you're not testing the circuit you're testing the RCD device..... ELI and IR tests should have already been conducted, so why would you want to test from a socket?? Almost ALL RCD manufactures recommend testing at the devices terminals where test results are going to be used for official records, eg EIC, EICR'S etc...
Eaton RCBO Pod being a good example of test anywhere BUT at the terminals... lol
Eaton RCBO Pod being a good example of test anywhere BUT at the terminals... lol
There are one or two types of RCBO pods that require a short length of conductor (say 6'' or so) to be connected to the device, think one of them is the MEM pods, but the vast majority you'd conduct RCD tests at the device terminals....
What's this 'Pod'? Is it some new technical term?
Reply to Testing Rcd in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net