Discuss Testing Ze using robin tester in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

Stress head

Hi recently purchursed a robin kmp 4116dl. It's came with no instructions so unsure testing Ze if it's a 2 or 3 lead instrument.
Thanks in advance
 
hawk81 im a trainee electrician , and i only do like for like fittings, pat testing, odd extra light so on, as you know electricians dont want any help at mo..
 
Hi recently purchursed a robin kmp 4116dl. It's came with no instructions so unsure testing Ze if it's a 2 or 3 lead instrument.
Thanks in advance
Iv got a ROBIN KTS 1620 i downloaded the instructions from kewtech as they bought them out and now there just re branded same meter.
If you ve got 3 leads you use 3, If you ve got 2 use 2. The 3 rd will be live and you dont want it dangling about :)
 
Hi
use the 3 lead for ze,zs,pfc,psc,rcd and then use 2 lead for continuity,Insulation testing you should have 2 sets of leads the set with 3 wires should be fused and the set with 2 unfused when using the 3 leads they will all be live testing so please take care my friend as that invisable thing called electricity stings

cheers
Rich
 
Last edited:
Kewtech instruments used to make identical machine to the Robins, and there instructions were identical as well, so try a download from kewtech.
Try emailing Fluke, as they own Robin, or they used to.

Cheer...........Howard
 

Reply to Testing Ze using robin tester in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

So, I was messing around yesterday with some old testers I have laying around to see if they still work I found my dads old Robin MFT and noticed...
Replies
8
Views
546
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
697
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
865
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
643

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock