Discuss The breaker on the right trips after anything from 30 seconds to an hour. I have only two led lights on this circuit in the DIY Electrical Advice area at ElectriciansForums.net

I'm not certain, but it appears to be a ground fault breaker. If I'm right, it is a special safety breaker that trips when there is overcurrent or when there is leakage to ground. I've seen situations where ground fault breakers will trip after someone cleans the area with a spray cleaner and gets some in an outlet, leading to leakage.

You're going to have to isolate the fault by finding every outlet on the breaker, disconnecting them one at a time, resetting the breaker, and seeing which one solves the problem. Then replace that outlet. If not solve the problem, it is defective wire. That is very rare.
 
Yes, in UK terms it’s an RCD. Tests for current leakage to earth on either the live or the neutral conductors.
The circuits being protected appear to be outside equipment, so it could well be moisture ingress or rodent damage.

Test the RCD using the button. If it doesn’t trip off, the RCD needs replacing.
Other tests can be performed but they include disconnecting the outgoing circuits, or using a specialist piece of equipment. Both would be safer being done by an electrician.
 
The breaker on the right trips after anything from 30 seconds to an hour. I have only two led lights on this circuit. Can anyone please help?

To clarify, do you mean the B20 circuit breaker marked "Patio", or do you in fact mean the RCD to the right of that (rather than a "breaker")?

The RCD is protecting both circuits, and will trip on an imbalance of L/N, e.g. leakage to earth. If one of the breakers is tripping, that will be due to overcurrent.

if the RCD is tripping, then turn off one of the circuit breakers, reset the RCD and check again to see if the RCD still trips. Repeat with the other circuit breaker. That may tell you which circuit is at fault (Gates or Patio).
 

Reply to The breaker on the right trips after anything from 30 seconds to an hour. I have only two led lights on this circuit in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Summary (TL;DR) Several lightbulbs in my home supplied by one circuit breaker dim over time and go out in about a year. Right now, the ceiling...
Replies
0
Views
731
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
878
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
871
Hi, I have two LED light panels (like this: LED Panel 120x30cm - Varm hvid 3000K-40W -...
Replies
2
Views
585
Hello I have recently moved home and I looking to upgrade lighting across the house to LED. In the kitchen I have found that there is installed...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock