I've just tested a sub-main cable running to an old barn. 0.05 Mohms at 250V. Obviously a fail, but the customer says it's fine because it works. As they're clearly not interested in their own safety I wondered if I could make them see sense by the cost. So my question is; How much does it cost them? Is it simply 240/ 50 000 to see the wasted current.

Thanks, Paul
 
Yes (for a purely resistive load) and it comes out (unless I've got my calculations wrong) as about 10-12 units of electricity a year. Not enough to justify any form of expenditure, but it could have serious safety implications which you should perhaps explain to them.

So, why were you testing the sub-main in the first place? The insulation resistance reading was 0.05Mohms... between what? L-N, L-E, N-E? Were all the readings consistent? Why did you not test at 500v?
 
I've just tested a sub-main cable running to an old barn. 0.05 Mohms at 250V. Obviously a fail, but the customer says it's fine because it works. As they're clearly not interested in their own safety I wondered if I could make them see sense by the cost. So my question is; How much does it cost them? Is it simply 240/ 50 000 to see the wasted current.
What cable was youa testing.
 
About one watt being dissipated if that's from the line conductor so about £1.50 per annum, nothing at all if it's from the neutral. But it's unusually low and points to some kind of damage. How long and what size is the cable? Could there be joints?

I think the way I would tackle it would be to point out that the low insulation resistance, although bad in itself, is a timely warning that there might be more serious trouble brewing that needs to be found before it destroys the cable.
 

Reply to The cost of poor insulation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Most of the work I do is additions and alterations in domestic properties, and other than swapping accessories and lights in new-builds for...
Replies
2
Views
2K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
5K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top