A 10mA RCD trips between 5mA and 10mA. A 30mA RCD trips between 15mA and 30mA. Any differential fault current that exceeds the tripping current of that particular 30mA RCD is equally likely to trip either or both RCDs.
You will only get discrimination if the fault current exceeds the tripping current of the 10mA RCD but is less than that of the 30mA one.
You can, of course, replace the 30mA RCD with a 'S' type delayed version, but then the rest of the circuits supplied by that RCD will not have the required level of protection.
When I do the experiment, I touch the phase to the earth wire. There is no resistance (resistance of the wires and the contact point) so the leakage current is maximal. I don't measured the leakage current, but let's say it's 1 A. The fault is located after 30mA and after 10mA RCD. So if the current reaches from 0A to 1A instantaneously, then both RCD will shut off. I'm thinking correctly? What if using a coil in second circuit to slow a little bit the current in the moment of connection and give time to the RCD 10mA to cut off?
 
When I do the experiment, I touch the phase to the earth wire. There is no resistance (resistance of the wires and the contact point) so the leakage current is maximal. I don't measured the leakage current, but let's say it's 1 A. The fault is located after 30mA and after 10mA RCD. So if the current reaches from 0A to 1A instantaneously, then both RCD will shut off. I'm thinking correctly? What if using a coil in second circuit to slow a little bit the current in the moment of connection and give time to the RCD 10mA to cut off?
Both RCD's are seeing the same amount of fault current (usually). It doesn't matter if you have a 1A RCD upstream of a 1mA RCD if the fault current is 500A! The only difference, as you've identified, is which trips first.

What you can get are auto-resetting RCD's such as Gewiss' exclusive intelligent RCD, resetting itself safely after a nuisance trip - https://www.voltimum.co.uk/articles/gewiss-exclusive-intelligent-rcd
 
Both RCD's are seeing the same amount of fault current (usually). It doesn't matter if you have a 1A RCD upstream of a 1mA RCD if the fault current is 500A! The only difference, as you've identified, is which trips first.

What you can get are auto-resetting RCD's such as Gewiss' exclusive intelligent RCD, resetting itself safely after a nuisance trip - https://www.voltimum.co.uk/articles/gewiss-exclusive-intelligent-rcd
Which trips first, that's the question.
Interesting I didn't know about existence of stuff device as ARD, intelligent RCD. Thanks for information
 
If you are touching phase to earth as an experiment, you are creating a massive fault current. I wouldn’t be surprised if the upstream 30mA is knackered now.

We are now getting away from one rcd covering several circuits to one RCBO per circuit. More expensive of course, but cuts down on nuisance trips.
Only the faulty circuit trips, leaving others on.
 
Which trips first, that's the question.
Interesting I didn't know about existence of stuff device as ARD, intelligent RCD. Thanks for information

It doesn't really matter which trips first. The point is that on a fault like you are describing both devices will start to trip. One may well take slightly longer to complete the operation, but both will trip once the operation has begun.
 
Extremely small amount of time is the key to my problem.
Logically, to measure any current, leakage current or normal current, we need a time, small amount of time. Now is to manufacturers to build different devices with different sensibility for different applications. I would like to identify the most sensitive RCB.
The electrical wires length in the house comparing to distance to the Sun is nothing, so I assume the speed of current is instantaneous, in my house. The distance between two RCB is too small to have any delay so the waveform is synchronous, I think.
For most intent purposes what we perceive as instantaneous can be described as such, especially such that our senses and reactions are way way slower than the speed in which electricity and light propagates.

But there is no such thing as a cause and effect mechanism which is instantaneous in the way you imagine it.
 
If you are touching phase to earth as an experiment, you are creating a massive fault current. I wouldn’t be surprised if the upstream 30mA is knackered now.

We are now getting away from one rcd covering several circuits to one RCBO per circuit. More expensive of course, but cuts down on nuisance trips.
Only the faulty circuit trips, leaving others on.
Yes, this in an experiment, test. In real life this happen when a defective device has a fault of insulation - the phase is touching the ground. I'm testing different electrical equipment that could have short circuit or leakage problem. I have seen equipments that works fine 5 minutes then when the resistance is hot it cause short or leakage to the ground and the general RCD switchs off.
Can you give me and example of what you are using to cut off only the faulty circuit? This is exactly what I need. Thanks
 
Yes, this in an experiment, test. In real life this happen when a defective device has a fault of insulation - the phase is touching the ground. I'm testing different electrical equipment that could have short circuit or leakage problem. I have seen equipments that works fine 5 minutes then when the resistance is hot it cause short or leakage to the ground and the general RCD switchs off.
Can you give me and example of what you are using to cut off only the faulty circuit? This is exactly what I need. Thanks

RCBOs are used to give earth leakage protection to individual circuits. They combine over current and earth leakage protection.

If one trips then you only lose that circuit, not the whole system.
 
It doesn't really matter which trips first. The point is that on a fault like you are describing both devices will start to trip. One may well take slightly longer to complete the operation, but both will trip once the operation has begun.
Here someone reported it managed to cut off only faulty circuit. This is why I'm searching for
 
RCBOs are used to give earth leakage protection to individual circuits. They combine over current and earth leakage protection.

If one trips then you only lose that circuit, not the whole system.
So you mean individual circuit is to have dedicated power outlet in the wall, one RCBO per outlet? Maybe at home this is possible to do. But at work or another home where you can't modify the main distribution board how to be? Any idea?
I have an idea - to build Arduino controled relay - 3 relays, phase, neutral and earth. The current sensor is measuring and comparing the current - if phase and neutral are equal - then OK, but if is detected very small leakage to earth, then the microcontroller shuts off all 3 relays. The Arduino processor and the Relay it is enough fast to perform this operation faster than regular RCBO on the market?
 
So you mean individual circuit is to have dedicated power outlet in the wall, one RCBO per outlet? Maybe at home this is possible to do. But at work or another home where you can't modify the main distribution board how to be? Any idea?
I have an idea - to build Arduino controled relay - 3 relays, phase, neutral and earth. The current sensor is measuring and comparing the current - if phase and neutral are equal - then OK, but if is detected very small leakage to earth, then the microcontroller shuts off all 3 relays. The Arduino processor and the Relay it is enough fast to perform this operation faster than regular RCBO on the market?

You're still missing the point that the other device has already started the tripping process.
 
Ive just noticed the OP is in France.... so not sure of how their regs demand when and where to have rcd protection.
 
You're still missing the point that the other device has already started the tripping process.
I understand this. In your opinion, it's impossible to do what I described above?
 
I understand this. In your opinion, it's impossible to do what I described above?

I wouldn't say impossible, but I think it would be very difficult to get reliable and repeatable results.
 
I think there is a company called Usain who make record breaking fast devices.
 
I think there is a company called Usain who make record breaking fast devices.
You think? Well, if you find the contacts of this company, please post here to help the community
 
  • Optimistic
Reactions: DPG
Think about it.
Thanks for suggesting a ''nice company who makes super fast breaking devices'', but I think about useful information that I got from another members. And you still think that there somewhere is this nice company or you can share with us more information about it?
 

Reply to The fastest RCBO in the world in the DIY Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock