Discuss The First Table in Section 7 of Onsite Guide.... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
8
The first table in the OSG, p64 (it has no table name). It says the following maximum loads are assumed per circuit, and then it lists circuits and their rating, along with Load.

My question, is this table showing maximum load that it's recommended these circuits should reach? Or is the Load they are speaking about in this table, the demand after diversity has been applied?

A tutor at college pointed us to this table and said it gives proper diversity on final circuits, but to me this seems not necessarily to be the case so I'm just trying to clear it up for myself so I can reference it in the proper way.

Thanks again in advance for any help.
 
The very first table is the maximum assumed load.

That whole section is about specifications for standard circuits so you don't have to worry about voltage drop, so the very first table specifies the assumed maximum load for the circuit. i.e. the value they've used in the voltage drop calculations for the current.
[automerge]1580972881[/automerge]
And if you're a trainee, we have a trainee only area. If you register as a trainee you'll get access.
 

Reply to The First Table in Section 7 of Onsite Guide.... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I'm a self-build amateur - I'll be running cables and getting system sign-off/inspection by certified competent person, and am just working...
Replies
6
Views
1K
Hi all. My first niceic assesment for joining is coming soon. I want to show my friends house where I installed new fuse board and installed new...
Replies
70
Views
7K
I installed outdoor lighting and outlets. I finished this past year. I passed my inspection on April 2022. I was so pleased, BUT now the circuit...
Replies
3
Views
912
Hi there, I'm just trying to get myself into cable calc and my first hurdle is demand and diversity. I understand the majority of what is coming...
Replies
1
Views
6K
This is my first post so please be gentle! I've been asked to extend an RFC into an extension at the back of an 8 year old property. It is a...
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock