Search the forum,

Discuss The wisdom of equipotential bonding in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
I'm probably displaying my ignorance here, but fortunately I'm not one of those people who can't stand to be laughed at!

I've been thinking a bit about one of those things I've tended not to dwell on. The technical reason for equipotential bonding is obvious - if you create equipotential zones, such that everything rises to the same potential in the event of a fault, then we reduce the risk of shock from touching simultaneously accessible conductive parts.

Very well. But doesn't it run the risk of simply making lots of conductive parts live to Earth instead of just a few? So instead of a bit of cable tray over there being live, they all are. So unless you're wearing thick rubber shoes...!

Doesn't it risk solving one problem and creating another?
 
Otherwise known as “Electricity was perfectly safe until we started earthing everything!”

It’s a bit of an all or nothing situation - you either build a system where safety is afforded by guaranteeing there’s no possible way to make a circuit under a fault condition or you build one that’s as efficient as possible in making that fault as big as it can be to make manufactured protection work. As there’s no money to be made in the first option we’re stuck with the second.
 
Otherwise known as “Electricity was perfectly safe until we started earthing everything!”

It’s a bit of an all or nothing situation - you either build a system where safety is afforded by guaranteeing there’s no possible way to make a circuit under a fault condition or you build one that’s as efficient as possible in making that fault as big as it can be to make manufactured protection work. As there’s no money to be made in the first option we’re stuck with the second.
I hadn't thought about the financial implications!

Thanks for that. So I'm not completely wrong then.

Edit: although isn't the idea that supplementary bonding reduces the shock risk in the event that manufactured ADS fails or isn't feasible for some reason? It seems to me that it risks causing everything to have a potential to Earth instead of just something.
 
Last edited:
So we have three extraneous parts in close proximity two of which are bonded together and to earth. The third is not and becomes live, what happens should you touch the live one and one of the others?
Connecting all parts together essentially makes them a whole single part assuming the resistance of those bonds are of a sufficient low resistance.
 
So we have three extraneous parts in close proximity two of which are bonded together and to earth. The third is not and becomes live, what happens should you touch the live one and one of the others?
Connecting all parts together essentially makes them a whole single part assuming the resistance of those bonds are of a sufficient low resistance.
Right, but if the fault current is insufficient to actuate your ADS, then you now have three live parts instead of two.

It's this business of them all rising to the same potential - potential to Earth. If your ADS does its stuff then you don't need any equipotential bonding do you. The idea certainly of supplementary equipotential bonding is to try to make it so that the fault doesn't create a circuit with you in it. But isn't there just an increased risk of you touching something live and making a circuit with the conductive mass of the Earth back to the transformer?
 
If you have three parts bonded together you essentially make it one part.
If you omitted bonding then my scenario in #6 becomes extremely hazardous.
Your last sentence I assume you mean touching a live part to an earthed part and of course this is a hazard which is why we can put in place additional RCD protection as an alternative.
 
I've wondered this. If there is a fault and it doesn't trip for whatever reason. Everything Earthed and Bonded is linked at the MET potentially meaning every exposed and extraneous (spelling) is live.

Now we are limiting our changes because probably the most common conductor? That has a good link to earth the water pipe is bonded and so at equal voltage. But little Timmy touching the the metal socket front during the fault in his bare feet?
 
All things being equal if your earthing and bonding is sufficient then along with circuit protection ADS is satisfied and little Tommy should be perfectly safe.
 
I've wondered this. If there is a fault and it doesn't trip for whatever reason. Everything Earthed and Bonded is linked at the MET potentially meaning every exposed and extraneous (spelling) is live.

Now we are limiting our changes because probably the main conductor? That has a good link to earth the water pipe is bonded and so at equal voltage. But little Timmy touching the the metal socket front during the fault in his bare feet?
Yes, you can see what I'm saying can't you. If your ADS does its stuff then happy day, but if it doesn't then absolutely everything rises to the supply voltage relative to Earth.

I do understand the principle of equipotential bonding, and these days of course, more often than not, ADS will save the day. However...
 
Well yeah before RCDs the MCB has to be at x3 - X5 and doesn't offer protection to life so yeah I've wondered this.

I'm guessing the main potential danger is touching the pipe at the same time as the fault is considered much more dangerous than other faults because of its good link to earth.
 
Back in the day, we had EEBADS… which specifically was EARTHED equipotential bonding and automatic disconnection of supply…. So if it wasn’t earthed, there was something wrong.
Do you have ANY idea of how much therapy you've just undone?! 🤣
 
There was a time everything would seem to get a green yellow wire. from the kitchen sink , the bathtub , all the pipes in and around the boiler and the immersion tank pipes etc. if it looked metal plumbers and builders would attach a green yellow wire to it.
 
Inside the equipotential zone pretty much the only things that are capable of introducing and earth path are the things that will be bonded anyway. Even if little Timmy touches something that is at 230V in bare feet it doesn't matter because the floor is pretty much insulated, it might be carpet or wood or whatever, the walls are insulated, usually plasterboard or similar, there is literally nothing other than the bonded stuff that can cause harm.

I remember years ago, before RCD's on lighting circuits and we were working in a house where the plumber was doing bits and pieces and he was putting plastic Tees into copper pipe work for new radiators and taps etc. The house owners dad (its always the dad isn't it) wanted me to bond across the plastic tees to keep the continuity of the pipework. I tried to explain that having a radiator isolated from the earthed plumbing system was a good thing rather than bad but he just wouldn't have it.

Just to add as well, I wonder whether many people realise that every time they touch anything that is earthed they are actually introducing 230v to their body via the N-E link somewhere, its only because the neutral side of the power is "bonded" to earth keeping it at the same voltage that they don't notice.
 
Inside the equipotential zone pretty much the only things that are capable of introducing and earth path are the things that will be bonded anyway. Even if little Timmy touches something that is at 230V in bare feet it doesn't matter because the floor is pretty much insulated, it might be carpet or wood or whatever, the walls are insulated, usually plasterboard or similar, there is literally nothing other than the bonded stuff that can cause harm.

I remember years ago, before RCD's on lighting circuits and we were working in a house where the plumber was doing bits and pieces and he was putting plastic Tees into copper pipe work for new radiators and taps etc. The house owners dad (its always the dad isn't it) wanted me to bond across the plastic tees to keep the continuity of the pipework. I tried to explain that having a radiator isolated from the earthed plumbing system was a good thing rather than bad but he just wouldn't have it.

Just to add as well, I wonder whether many people realise that every time they touch anything that is earthed they are actually introducing 230v to their body via the N-E link somewhere, its only because the neutral side of the power is "bonded" to earth keeping it at the same voltage that they don't notice.
I guess that's a whole other can of worms the fact that the Neutral is Earthed at some point.

I mean there are concrete floors and conservertries, garage floors etc
 
It comes down to what are the risks you are looking to avoid and under what circumstances.

Equipotential bonding avoids the risk of two or more parts having significant difference in voltage between them, but does not deal with the issue of the (now single) conductive assembly being at a different potential to anything else, such as the Earth.

RCD protection helps in many cases as if you have an open E/CPC, or high-ish impedance earth (such as TT case) you still have a good chance of ADS happening with leakages (hopefully before you are the leakage path). However, in the open-PEN case with TN-C-S it makes no difference as the RCD sees the L-N differences, not a sign of any current flowing in the CPC network that would give away the situation.

This has been the dirty secret of modern electricity networks until recently (except for a few special areas like marinas, etc). Now the prevalence of EV has thrust the risks of an energised car being washed outdoors in to the spotlight and so we now see open-PEN protection devices as stand-alone, or in a charger, chargers demanding TT earths, etc.

Ultimately you have trade-offs, a TN earth allows OSCP disconnection in most cases, adding a 2nd protection to RCD that TT lacks, while TT has no issues of open-PEN faults, but often they have a "single point of failure" in the RCD/RCBO electronics. You pays your money, you take your chances...
 
Euipotential bonding avoids the risk of two or more parts having significant difference in voltage between them, but does not deal with the issue of the (now single) conductive assembly being at a different potential to anything else, such as the Earth.
Yes, this is the problem I was referring to. In the event of ADS failure, you're simply increasing the chances of touching something with a potential difference to Earth, whilst obviously mitigating the risk of completing a circuit between simultaneously accessible parts. Solving one problem but creating another.
 
Yes, this is the problem I was referring to. In the event of ADS failure, you're simply increasing the chances of touching something with a potential difference to Earth, whilst obviously mitigating the risk of completing a circuit between simultaneously accessible parts. Solving one problem but creating another.
Again it depends upon the circumstances as to which is a greater risk.

All class I products are earthed, so any with external metallic parts will be CPC bonded anyway and touchable. Under ADS failure, or open-PEN fault, they might become live and if there is a real possibility of them being simultaneously touched with another Earth-connected item then you have a shock risk.

Indoors that item-item touching is far more likely than the outdoor example of touch EV and the true Earth simultaneous, and typically building have a few obvious items such as metallic service pipes, significant building steelworks, etc, that can and usually do introduce a separate connection to the Earth that may become different from the Earth-referenced CPC system, so bonding makes sense as the added risk is tiny compared to the mitigated risk.
 
I remember years ago, before RCD's on lighting circuits and we were working in a house where the plumber was doing bits and pieces and he was putting plastic Tees into copper pipe work for new radiators and taps etc. The house owners dad (its always the dad isn't it) wanted me to bond across the plastic tees to keep the continuity of the pipework. I tried to explain that having a radiator isolated from the earthed plumbing system was a good thing rather than bad but he just wouldn't have it.
I remember a case where an unbonded radiator in a kitchen had the lead from a radio permanently hanging down behind it. The lead deteriorated over time, as a result of the heat and sharp edges of the radiator fins and the radiator became live.
A child placed one hand on the radiator and the other on a nearby metal electric kettle, and was electrocuted.
This clearly wouldn't have happened if the radiator had been bonded to the kettle.
 
I remember a case where an unbonded radiator in a kitchen had the lead from a radio permanently hanging down behind it. The lead deteriorated over time, as a result of the heat and sharp edges of the radiator fins and the radiator became live.
A child placed one hand on the radiator and the other on a nearby metal electric kettle, and was electrocuted.
This clearly wouldn't have happened if the radiator had been bonded to the kettle.
Thats a freak accident though, it could just as easilly been anything that killed him. It could very well have been a double insulated bench grinder that damaged the flex which then came to rest on the body of the grinder, that too would just as easily become live and complete the circuit if you touched it and the kettle together, not a fault of badly designed electrics.
 

Reply to The wisdom of equipotential bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...
Replies
2
Views
2K
Just thoughts Id share my recent fun and games on my parents farm.. The electrics are old. Its a 400yr old house with outbuildings just as old...
Replies
9
Views
2K
I've got a bunch of old single phase BS88 1970s fuseboards in the communal areas of a converted building. All the wiring is MICC and it's buried...
Replies
9
Views
1K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock