Bessie

My customer's house has two consumer units connected in parallel. The first one supplies several ring circuits and already had an RCD. The second supplies several lighting circuits, washing machine, microwave, boiler and immersion heater - until I upgraded it, there was no RCD, just a 100A switch.

I checked insulation resistance on both boards before fitting the RCD - all circuits tested out OK, although one circuit on the board with the new RCD was a tiny bit under 2MOhm. Also tested the new RCD, likewise OK. I thought the job was done however customer rang the next day to say the new RCD keeps tripping.

Sure enough, half the times he turns on the microwave the RCD trips. Fair enough, maybe the RCD is faulty after all and a bit over sensitive, but what I can't understand is that when he boils the kettle on the kitchen ring circuit (remember, this circuit is connected to the other board via its own RCD) the new RCD trips even though it doesn't protect this circuit and belongs in a different board!

Is this a recognised phenomenon? Does anyone now what is going on here?

Thanks.
 
Try an IR test from neutral on one board to earth on the other board and vice versa when they are both isolated.
Running a high current item that trips an unrelated RCD tends to indicate a fault on one of the circuits the RCD protects and the high current is passing enough through the fault to trip the RCD.
 
A cct fault is likely. If nothing found then perhaps a hunt through the affected ccts to secure no borrowed or crossed neutrals (result of some diy?). No problem till RCD installed. Just a thought. Cheers.
 
Try an IR test from neutral on one board to earth on the other board and vice versa when they are both isolated.
Running a high current item that trips an unrelated RCD tends to indicate a fault on one of the circuits the RCD protects and the high current is passing enough through the fault to trip the RCD.
Thank you Richard and everybody who posted advice - it all helped! After reading your comments, the solution was quite obvious - I had forgotten to mention that, before I could install the RCD, I had had to bypass one of the original lighting circuits which had an earth-neutral short in the supply cable. I had disconnected the live feed at the CU but left the earth and neutral still attached, so current still leaking from neutral to earth - I just disconnected them at the CU. As you pointed out, it just seemed to be the high current devices on any circuit which caused the RCD to trip - lighting circuits weren't a problem.
 

Reply to The Wrong Rcd Keeps Tripping! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
795
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock