Hi all

I have just completed an electrical installation consisting of 2 ring circuits, 3 lighting circuits, fire alarm circuit and a heating circuit. All went well apart from the heating circuit.....

I have installed 2 electric thermostatic panel heaters, a 500w and a 750w one. They are in two offices and within 10m of the distribution board. The total load therefore is about 5.5A. I decided on a B6 MCB, 1.5mm twin&earth cable on a radial circuit and connected then via individual FCUs. I used a 3A fuse on the 500w and a 5A fuse on the 750w heater.
All dead testing , continuity, insulation resistance, polarity etc was all ok. Live testing was also ok.

My problem is this....
As soon as the 750w heater asks for power, i.e. turning the thermostat up, it trips the RCD but MCB does not trip. I did try a bigger MCB but same response.

I have spoken with technical support at Dimplex and told them the wiring design. They advise it could be a faulty heater and to return it.
Before I do this does anyone else have any other thoughts as to why this would happen...

I am probably missing something really simple but can someone please advise as soon as possible.

Thanks
 
--A well earthed metal sheet-- (Sheet is a good word)
Not sure about dimplex but some cheap ones not much more than a metal sheet with " Electric blanket wire"
Held down by alloy tape .
Usualy get a nice hole in tape if no RCD !
(I was very dissapointed - cheap in china ? )
Tech has moved on - 3M tape very sticky .
2x power settings 2x circuits .....
( I'm hoping some one will correct me and )
( say things have got much better -mats/pads ? )
 
You specifically state that when the 750w powers up, the RCD trips... does the same thing happen when the other unit powers up? Are they both on the same thermostat? If not, is it possible the wiring in the stat is wrong?
 
Thanks

Both on the same radial circuit.

I think I will have to double test the continuity of the circuit again. r1 rn and R2

Both heaters are tripping the RCD as I found out today so must be the wiring.

Cheers

Martin
 

Reply to Thermostatic panel heaters in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
230
Hi all, I have an Economy 7 storage heater Dimplex CXL24N - 3.4kW Storage Heater + Convector ( there not available anymore) that dos'nt work and...
Replies
1
Views
565
Hi All I have been asked to supply a minor works certificate on a smart thermostat upgrade. Would I just test the dedicated circuit from the CU...
Replies
3
Views
301
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
262

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock