Discuss Three phase cable to wire single phase in the Australia area at ElectriciansForums.net

Safely terminate the spare cores
ensure you have marked the cables in use with correct colour sleeves

edit, just been pointed out to me that this is not a U.K. issue.
above is what we would do over here normally.
can’t be certain if it’s suitable advice for down under.
 
Last edited:
Can I use three phase cable to wire single phase
James is correct with some caveat.
So the answer is YES...NO
The below examples would be as per AS/NZ3000 regulations:
I have done so where it was used as a submains where you used the 4 wires to double up on Active/Neutral to reduce the Voltage drop. Here a separate remote earth is used..so no problem.
If you would want to use it to increase the current rating...lets say for 15A Outlets on 2.5mm2 cable...then you have to add an additional separate earth wire. Most Electricians would snub their nose on this....but it is certainly within regulations.
So its not a colour code problem as long as they are identified what are actives and what are neutrals as per Jame's reply.
 

Reply to Three phase cable to wire single phase in the Australia area at ElectriciansForums.net

Similar Threads

Looking to use this brooks Compton motor as a replacement in an electric cement mixer. can anyone tell me if it is designed to operate off a...
Replies
2
Views
615
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
840
Lou submitted a new resource: Aclara SMETS2 Single Phase/SMETS2 5 Terminal Meter Manual - The manual for Aclara SMETS2 Single Phase/SMETS2 5...
Replies
0
Views
209
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
282
I have a single phase stainless steel pasteuriser that has two control boxes attached to it. One box houses the control for the electronics and...
Replies
2
Views
680

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock