Discuss three phase rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
236
Hi guys.

Can anyone explain in simple-ish terms how a three phase rcd measures a currents imbalance? It can't be between phases as not all three phase systems are balanced equally so it must be between phase and neutral big how?

Just curious!
 
It measures the same as you would clamp a 3 phase circuit with your earth leakage clamp meter to test for leakage. If it's 3 phase no neutral then the sum of all the currents flowing simultaneously in the 3 phases will equal zero if there's no leakage. Likewise with a 3 phase and neutral circuit except the neutral current must also be included in the zero sum equation.

Current in will always equal current out.
 
Last edited:
interesting if its not a balanced load then it will need a neutral so yes any in balance between line and neutral would trip the rcd but im interested myself to here other peoples versions of how a balanced load with no neutral would trip the rcd
 
exactly equal currents in each phase means the the current in the neutral is Zero
 
marvo if say there was 10amp on each phase so 30 amp total how would this equal zero ive had this explained to me a while ago but scratching head trying to remember lol

Because the voltage phase angles of each phase are 120 degrees apart so when current is flowing one direction in one of the phases it's flowing in the opposite direction in at least one of the other phases.

Current flow in a circuit is a physical thing like water flow in a pipe, an Amp by definition is a Coulomb of electrons flowing past a point in one second and a Coulomb is an actual number of electrons. You can picture an Amp of current flow as being similar in nature to a litre per second of water flow in a plumbing circuit so if a quantity of electrons (current) is flowing one direction in one leg of a circuit an equal quantity of electrons (current) has to be flowing out of the circuit.
 
An RCD can theoretically work on any number of conductors, so long as every conductor in the circuit has its own sensing winding on the RCD transformer. A single-phase RCD has two windings, a 3-phase has four, you could make one with six windings for 5-phase power!

Farm, visualise a 3-cylinder radial aero engine, with all three con-rods sharing a crankpin. The positions of the pistons represent the currents / voltages on a balanced 3-phase system - the moving mass of each piston is balanced by the sum of movements of the other two.
 
thanks marvo wow your first explanation was easier ha ha cheers
Lol, I'm trying to keep it simple, honest.

If you understand how a single phase RCD works then you should be able to get how a 3-phase RCD does. It's basically a current transformer where current through the circuit conductors all cancel each other out so they balance which means that no current is induced into the sensing winding. It's only when there's leakage to earth that they no longer balance and it's this imbalance that causes a current in the sensing winding which in turn operates the mechanism that causes disconnect.

RCD Arrangements.jpg
 
My tradesman got caught out by one of these the other week. Scratching his head why the 30A 3-phase drives were running fine but a piddly little burner tripped the 200A main switch every time. Turns out another worker had left the neutral out of the main RCD.
 

Reply to three phase rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
996
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
746
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
TT system, existing three phase fuse board recently installed by another spark which only has single phase circuits terminated into individual...
Replies
15
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock