Discuss Three Phase wired machine ohms law calculation in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I have a machine which is wired as 3 phase neutral and earth and is 15.1KW, there are no 415v components and all components are 230v, so effectively it is using 3 single phase circuits, however I have always carried out the circuit breaker calculation based on the 415V potential, I.E> 15120W divided by 415V =36.43 therefore I would fit a 40Amp 3 phase breaker, I have been told by the manufacturer that I have incorrectly calculated this and should divide this calculation by 3 to calculate the correct 3 phase breaker and i should fit a 12A 3 phase breaker, I am not convinced that this is correct but am now second guessing myself, can any one assist.
 
I have a machine which is wired as 3 phase neutral and earth and is 15.1KW, there are no 415v components and all components are 230v, so effectively it is using 3 single phase circuits, however I have always carried out the circuit breaker calculation based on the 415V potential, I.E> 15120W divided by 415V =36.43 therefore I would fit a 40Amp 3 phase breaker, I have been told by the manufacturer that I have incorrectly calculated this and should divide this calculation by 3 to calculate the correct 3 phase breaker and i should fit a 12A 3 phase breaker, I am not convinced that this is correct but am now second guessing myself, can any one assist.
What machine are you speaking of?
 
15kw in star configuration is the same as 3 x 5kw loads on separate 1ph supplies.
5kw /230v = 21.7A

15kw /400 / 1.732 =21.65A

if they are all running off a single phase supply then its 15kw / 230 =65.2A

the manufacturors instructions should have the supply requirement printed in them.
if they are wrong, then after you have advised them then its there problem???
 

Reply to Three Phase wired machine ohms law calculation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
844
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
2K
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock