Hi, I'm new here, and really hope for advice... Could anyone kindly put me in right direction. How do I go about connecting the second switch on landing, or what have I done wrong so far (attached image)? Whatever is connected now works a treat.

Thanks for your time :)

LIGHTS.PNG
 
IMG_7350.PNG

Try this. It's all on there
You need a 2way switch at each end and a intermediate switch in between. You can add as many intermediate switches as you like providing you have a 2way switch at each end.
 
It is possibly worth pointing out that your original diagram shows each switch to be a double gang two way switch as you have duplication of each of COM L1 and L2.
You would need to have one of your switches as an intermediate switch. Also each switch (if the whole arrangement is only switching the one light) would only need to have a single gang i.e. one switch on each plate.
With the current arrangement you have shown you are lucky if it works correctly as you are splitting the circuit over two different gangs in the same switch plate.
I would start from new for the connections.
 
I believe in the on site guide it does show the black as common and brown as L1.
I might be wrong, I know I've seen it in one of the regs books.
some guys i work with used the black as neutrals, that used to wind me up because they wouldnt bother sleeving them or telling anyone else on site who was using the black as you guessed it, switched live!

the way i see it is if 3 phase conductors are identified by brown/black/grey in that order, then it still kind of applies when you have 3 live conductors of a 3core+e , if brown is common then switch wire/strappers should then be l1=black l2 = grey

not often i have a 3core between 2 ways, feed at one end, switch live at other end and t+e for strappers
 
I believe in the on site guide it does show the black as common and brown as L1.
I might be wrong, I know I've seen it in one of the regs books.
some guys i worked with used the black as neutrals, that used to wind me up because they wouldnt bother sleeving them or telling anyone else on site who was using the black as you guessed it, switched live!

the way i see it is if 3 phase conductors are identified by brown/black/grey in that order, then it still kind of applies when you have 3 live conductors of a 3core+e , if brown is common then switch wire/strappers should then be l1=black l2 = grey

not often i have a 3core between 2 ways, feed at one end, switch live at other end and t+e for strappers
 

Reply to Three Way with Intermediate and Three Wire in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

FYI --- This is a U.S. installation. I'm replacing a three way switch (the UK might more sensibly call it a two way switch??) with a Kasa Smart...
Replies
4
Views
783
I've got a security light which has two wires like a normal ceiling lamp (the first wiring diagram attached). I bought a new security light which...
Replies
7
Views
2K
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
336
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
871
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
507

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock