I have been a sparks for 30 odd years ,I did my 3 years at college for my 2361 1&2
I have my 16th and my employer does not trust my work now because I'm not 17th soon to be 18th . I was off work and they called in another sparks . He sorted the problem out and said my work was dangerous.
I had a 32a bracket on 2.5 twe supplying 2 x 16amp toasters , I put an amp meter on them and they were pulling 12 amps each. So I know they were fine.
But because this new sparks said I did not have 17th , I could not do any more electrical work.
I work on commercial site .
Has the regulations changed that much ?.
So it's time to say goodbye to a trade I have loved doing for 30 years and will miss it.
Good luck to all the newbees coming into a brilliant trade and look forward to all the new friends you will make .
 
Not sure what you mean by a 32A bracket?

However I must cringe at the very notion of T&E being used in a commercial setting - that cable is designed for domestic use only.
 
If you mean you supplied a single 2.5 twin and earth via a 32 amp breaker then yes that is dangerous.16amp or 20 amp breaker at a push.And i agree that tw&e cable is not really suitable for commercial use.
 
Not sure what you mean by a 32A bracket?

However I must cringe at the very notion of T&E being used in a commercial setting - that cable is designed for domestic use only.
Think he means breaker and sorry I agree it should not have been on a 32A.
Didn't know BS6004 only designate this cable for domestic use, learn something new everyday.
 
If you mean you supplied a single 2.5 twin and earth via a 32 amp breaker then yes that is dangerous.16amp or 20 amp breaker at a push.And i agree that tw&e cable is not really suitable for commercial use.

You can actually have a 2.5mm conductor in a 32A MCB as long as it is only supplying one single or one double socket. That scenario couldn't be applied here but just mentioning it.
 
What is wrong with T&E on a commercial site or does everyone wire offices in swa now.
 
You can actually have a 2.5mm conductor in a 32A MCB as long as it is only supplying one single or one double socket. That scenario couldn't be applied here but just mentioning it.
I beg to differ.2.5 cable can take a max of 27 amps if clipped direct.23amps in a wall or 21 amps above a plasterboard ceiling with insulation.Putting a 2.5 on anything bigger than a 20amp breaker would be madness.Personally i would put a 16amp breaker feeding it.If you wish to back up your claim then please quote the relevant BS7671 number.
 
You could have 2.5mm^2 T&E on a 32A breaker if overload protection has been omitted (fixed load). Don't know why you'd do it though. T&E is not strictly for domestic use only, it is used extensively in offices, shops etc. It probably should be though. To me, it depends on the setting, I hate seeing it in commercial kitchens, for example, or factories etc.
 
Not sure what you mean by a 32A bracket?

However I must cringe at the very notion of T&E being used in a commercial setting - that cable is designed for domestic use only.
Sorry I call it commercial as it's 9 buildings not a factory. Yes I hate predict text. 32amp breaker supplying a small 2 way board and 16a mcbs in turn each mcb supplying a toaster.
Sorry for the misunderstanding.
Have the regulations changed that much ?
 
Think the 2.5 on 32amp mcb is referred to a spur off the existing ring final circuit which can feed a single or double socket as the idea is the spurred 2.5mm clipped direct at 27amps can't be overloaded
 
Sorry I call it commercial as it's 9 buildings not a factory. Yes I hate predict text. 32amp breaker supplying a small 2 way board and 16a mcbs in turn each mcb supplying a toaster.
Sorry for the misunderstanding.
Have the regulations changed that much ?

I'd have that submain on 4mm^2 at least.
 
I beg to differ.2.5 cable can take a max of 27 amps if clipped direct.23amps in a wall or 21 amps above a plasterboard ceiling with insulation.Putting a 2.5 on anything bigger than a 20amp breaker would be madness.Personally i would put a 16amp breaker feeding it.If you wish to back up your claim then please quote the relevant BS7671 number.

So spurs are banned in your opinion then ? And it's perfectly acceptable to take a RFC spur from the 32a MCB, only feeding one socket though as HHD rightly stated.
 
Sorry I call it commercial as it's 9 buildings not a factory. Yes I hate predict text. 32amp breaker supplying a small 2 way board and 16a mcbs in turn each mcb supplying a toaster.
Sorry for the misunderstanding.
Have the regulations changed that much ?
No the breaker would be oversized it has nothing to do with recent changes.
 
I get the ring final spur but why are people justifying, creating scenarios pushing this cable size to its limit when in reality they wouldn't do it.
 
I beg to differ.2.5 cable can take a max of 27 amps if clipped direct.23amps in a wall or 21 amps above a plasterboard ceiling with insulation.Putting a 2.5 on anything bigger than a 20amp breaker would be madness.Personally i would put a 16amp breaker feeding it.If you wish to back up your claim then please quote the relevant BS7671 number.
I shall take the challenge :). I haven't got the BYB with me so I cant give you the exact page but if you take a look at appendix 15, reg 433.1.5, fig 15A and read under the 'unfused spur' title it will say:

"An unfused spur may be
connected to the origin of the
circuit in the distribution board."

If you think about it, it's exactly the same as spurring of a ring. As Ian has said, it cant be overloaded as the CCC is 27A clipped direct and fault protection is easily met with a 32A MCB. Plus.... It is in the regs as above.
 
Last edited:
No the breaker would be oversized it has nothing to do with recent changes.
Hi , I had one 32a mcb spare in the main board and needed 2 separate 16a mcb to supply 2 catering toasters.Not domestic.
So maybe it was wrong . Maybe it is time to bow out .
Thanks for your input
 
I get the ring final spur but why are people justifying, creating scenarios pushing this cable size to its limit when in reality they wouldn't do it.
Because this is a forum, and they can. ;)
But undersizing the cable then using the regs to back up the decision is pointless if you ask me.
 
I shall take the challenge :). I haven't got the BYB with me so I cant give you the exact page but if you take a look at appendix 15, reg 433.1.5, fig 15A and read under the 'unfused spur' title it will say:

"An unfused spur may be
connected to the origin of the
circuit in the distribution board."

If you think about it, it's exactly the same as spurring of a ring.

I said the same or very similar in post #13 HHD, in your defence. :)
 
"An unfused spur may be
connected to the origin of the
circuit in the distribution board."

If you think about it, it's exactly the same as spurring of a ring.

Your original post didn't mention spurs.You said you could run a double or single socket directly off a 2.5 fed from a 32amp breaker.in that specific case i would say thats unacceptable.If you were wiring the socket from scratch you would fit a 16amp breaker to feed the double or single socket.
 

Reply to Time to call it a day in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Folks , Just looking for a bit of advice as I'm looking to get back on the tools so please bare with me if this is a bit long winded. I'm a...
Replies
1
Views
619
Summary (TL;DR) Several lightbulbs in my home supplied by one circuit breaker dim over time and go out in about a year. Right now, the ceiling...
Replies
0
Views
736
In July I moved into my new home with Schluter DITRA heated floors in the bathroom. The floor quit working in December, and my GC and a rep from...
Replies
0
Views
353
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
637
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
560

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock