Discuss Timeclock Tripping RCD in the Electricians' Talk area at ElectriciansForums.net

E

earthboy

I have a 6A C Type RCBO feeding a Horstmann 20A Timeclock and the switched-line operating AC1 on a 4P 24A contactor (NO).

There are three lighting circuits going into the contactor, all fed from individual 6A B Type MCBs (on the RCD side of the DB).

Why should the RCD sometimes trip when the timeclock switches off? I say sometimes because when I try to reenact the tripping by either rotating the dial or operating the override switch, the RCD (most of the time) does not trip. I've yet to experience the RCD tripping when the lighting circuits are switched on.

The lighting circuits have low loads (2 x 58W fluorescent on one, 2 x 9W CFL on another and 3 x 20W CFL on the third).

All cabling and accessories are new, and all test results show no issues - the RCD operating times all fall within regulations.

Any suggestions?
 
Could it be something to do with the neutral connections? If you have an RCBO presumably fed from the main switch side to control the clock and contactor and your circuits fed from an RCD, there might be a slight imbalance. Can you wire the control circuit from the same RCD side of the consumer unit?
 
You have very low loadings, why do you need a contactor, or need to individually breaker the circuits ?

Try running the lot off the timer feed, switch only the line and see what happens.

Could be the RCBO don't like the contactor, back EMF from coil etc. It shouldnt trip, but might just be one of those weird ones. Might also not like capacitors in fittings discharging.
 
A contactor is sometimes required for automated lighting systems. I do showrooms for a certain company that leaves selected parts of the showroom lighting on controlled by t/switch & contactor. At a selected hour when the staff have gone home, the t/switch knocks the lights off.

Also, I fit contactor controlled lighting in their offices where one light-switch turns the whole of the lighting off.
 
Thanks for all your replies.

I think I will try swapping the timeclock feed RCBO and put the circuit back on a MCB on the RCD-side of the board and see whether this resolves the tripping.
 

Reply to Timeclock Tripping RCD in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
841
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
795
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
442
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock