Discuss TNCS CPC not used in the UK Electrical Forum area at ElectriciansForums.net

There is nothing to stop anyone adding earth rods to a TNCS system. Amendment 2 mentions this.
The real questions are probably:
-is it TNCS system?
-does the earth rod have a specialist purpose that needs to be understood?
Feel free to stick some photos up.
(Obviously, measuring what you think is the external loop impedance from the supplier, as well as the L-N loop impedance would help.)
 
They could have got there by many different means: it could have been TT and DNO now converted to TN-C-S, or it could still be TT if there was reason(s) to want to avoid the supplier's earth (for example, it feeds extensive outdoor metalwork, areas where PME is prohibited, etc).

As @timhoward says there is no harm, and often a small advantage, in adding rods to the supply earth, so if it simply is that situation then nothing really needs changing.
 
What type of installation is it? In certain circumstances such as temporary supplies to building sites the DNO can put in a TNCS supply but with hold the earth connection so that the site has to TT it.
 
Hi All,
As mentioned, I’ve got what looks like a TNCS system but CPC is coming via an earth rod???? Not tested TNCS system yet to see if earthing is acceptable
CPC or Main Earth?
 

Reply to TNCS CPC not used in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
531
Hi all - relatively new to Solar but I’m looking for opinions on fitting DC SPDs on a TNCS installation. Are we just earthing the SPD from the...
Replies
0
Views
457
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
A recent discussion on conduit choice wandered over to pros and cons of the 'conlok' style and a link was posted to one of the Efixx videos in...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock