Discuss TNCS export to out buildings in the UK Electrical Forum area at ElectriciansForums.net

bill01803

-
Esteemed
Arms
Reaction score
391
I have a house to test soon that has several sub-mains to out buildings, some t&e and some 2 core swa, and one to a swimming pool. The supply is TNCS and I know it should not be exported anywhere but what code should each one get on the EICR?
 
The one to a swimming pool should get special attention, I think. There is a specific risk there (the swimmers connection to the general mass of the Earth getting out of the pool) and I might C2 that one.
 
Pme can be exported as long as the bonding arrangements are adhered to
As for the swimming pool have a look in part 7 of bs 7671 as swimming pools are listed in special locations and follow what the regulations say.
 
Judging from the news this lunchtime we certainly won't be exporting any PME to the EU anytime soon, or anything else. I agree with Westy though, if you are asking these questions do you think you have the experience to undertake this, really?
 
I have a house to test soon that has several sub-mains to out buildings, some t&e and some 2 core swa, and one to a swimming pool. The supply is TNCS and I know it should not be exported anywhere but what code should each one get on the EICR?

Kindly enlighten me with the relevant regulation from Bs7671.
 

Reply to TNCS export to out buildings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

What are peoples opinion's on this, pair of big old semi-detached houses (85 and 87) converted into apartments, dont think its a HMO although it...
Replies
1
Views
262
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
741
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
494
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock