They are type 4 Federal Electric devices and you need manufacturers data to compare Zs values. Sounds like you are out of your depth on this.
I’ve came across this type of DB before, and it had some newer mcbs fitted along the old ones, but they had to cut the lid of the DB to make them fit, unless they’ve put the wrong ones in and bodged it...

A3CA85F7-22DD-4F13-81F1-513579A3B30C.jpeg
 
717 or 721 are you not still in the same boat, or should I say caravan as the requirements regarding TN-C-S apply in both cases.
 
I have worked extensively in the static caravan park world. The only acceptable earthing arrangements for such buildings is TNS or TT.
TNCS can be used for supply upto external plastic meter box. Unit itself must be connected to earth rod and fed via 30mA RCD. I have also worked on units with SEB TNCS supplies housed in external meter cupboards. We never used the company earth and always fitted earth rods usually one was enough but quite often would fit 2 1 at each end of the concrete base and always tested the metal chassis and side walls to the earth connection.
 

Reply to TNCS PME on caravan site with static caravan EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
875
There’s been a few recent threads about caravans, caravan sites etc, and I thought I’d post up some photos I took today while on one such site...
Replies
0
Views
884
  • Locked
I've been testing a static caravan installation. At the plastic meter box outside the 'van (which contains an RCD, 16A MCB, meter and 16A socket...
Replies
3
Views
2K
I'm doing an EICR on a static caravan after being called on to fix to a couple of problems due to loose connections. It's all fine now within...
Replies
4
Views
6K
Hi guys, Have a job on next week for a friend, my usual industry is maintenance so want to be sure I am checking all the boxes here. He...
Replies
53
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock