Search the forum,

Discuss To change DB or not ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
18
Evening all.
EICR done on ground floor flat all electric no gas, flats built 2006, no rcd protection on circuits 1 to 8 - lighting, kitchen appliance sockets , immersion ,panel heaters and towel rail, 3 storage heaters via contactor and rcd control 2nd immersion, general sockets, all cables installed within metal stud plaster boarded walls, 3 points that are visible show no grommets and butchered holes in metal frame with cables down to accessories , no supplementary bonding through out bath room. All insulation readings clear as a bell.

C2 no rcd protection on towel rail, bath room light and fan, shaver point and cables within metal stud,
Or C3 improvement

Thanks all in advance
 
C2 for no RCD for any bathroom circuits where there's no supp.boding.
C2 for cables in metal stud with no RCD.
C2 for kitchen sockets, no RCD.
C3 for no RCD lighting circuit/s.
 
C2 for no RCD for any bathroom circuits where there's no supp.boding.
C2 for cables in metal stud with no RCD.
C2 for kitchen sockets, no RCD.
C3 for no RCD lighting circuit/s.
Cheers Tel.
DB change then , told me gaffa this and was told it was wired to previous regs so it passes 14 apartments wired like that. Am I right in saying early 17th edition regs .
 
late 16th. irrespective of whether it complied the, your EICR is to determine if anything is dangerous or not. you inspect to current regs. any C1 or C2 issues must be rectified to get asatisfactory report.
 
Cheers Tel.
DB change then , told me gaffa this and was told it was wired to previous regs so it passes 14 apartments wired like that. Am I right in saying early 17th edition regs .

Your boss had a worrying outlook. How many other 'successful' EICRs has he done like this I wonder?
 
The Best Practice Guide #4 covers many of these points:

But as @telectrix said you consider it relative to the current regas and code any discrepancies based on the sort of risk they present from C1 to C3.

For an installation that is good to its original standard then the usual issues are the lack of RCD protection, the risk from that of course depends very much on the details of what the circuits are and where they power. But also the occasional unexpected points such as immersion heaters without a safety cut-out thermostat to BS EN 60335-2-73
 

Reply to To change DB or not ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top