Discuss To crimp or not? in the UK Electrical Forum area at ElectriciansForums.net

Rockingit

-
Mentor
Esteemed
Arms
Supporter
Reaction score
6,447
Finding myself doing a number of terminations at the moment where the cable dia (16-25-35mm) is at the smaller scale for the clamp or screw terminations they're going in to, so they're flattening or splatting more than I'd like. Toying with re-doing them using ferrules but I know there's two schools of thought on this - what are other people doing these days?

NB - not talking about fine stranded/tri-rate etc, just normal stranded singles/tails
 
Could you use the old technique of twisting a strand around the cable to keep the cores bunched and increase the size? :)
I have in the past used finger lugs or reducing lugs and ferrules for that size of cable but it depends, what size terminal are you trying to get them into are we talking way larger like 50-70mm?
 
Could you use the old technique of twisting a strand around the cable to keep the cores bunched and increase the size? :)
I have in the past used finger lugs or reducing lugs and ferrules for that size of cable but it depends, what size terminal are you trying to get them into are we talking way larger like 50-70mm?
I still do this today. The 35mm bond is rock solid.
20190601_160506.jpg
20190604_153034.jpg
 
Ferrules are a start, though they are thin and more about keeping the strands together to face up to the clamping force. I prefer to use tri-rated for those sizes if at all possible to make wrangling them easier, so ferrules are a must in my case.
 
Finding myself doing a number of terminations at the moment where the cable dia (16-25-35mm) is at the smaller scale for the clamp or screw terminations they're going in to, so they're flattening or splatting more than I'd like. Toying with re-doing them using ferrules but I know there's two schools of thought on this - what are other people doing these days?

NB - not talking about fine stranded/tri-rate etc, just normal stranded singles/tails
Are you using the right crimps and crimpers for the particular cable you are trying to crimp the lugs on?
 
Could you use the old technique of twisting a strand around the cable to keep the cores bunched and increase the size? :)
I have in the past used finger lugs or reducing lugs and ferrules for that size of cable but it depends, what size terminal are you trying to get them into are we talking way larger like 50-70mm?
Yes, terminals designed for 125-400A kind of stuff.

I'd forgotten that old technique of twisting a strand around the others, seems like a faff though?
 
To be fair wrapping a strand around is a bit of a faff if you have several to be done in one go but for the odd one is quite satisfying.
 
Cord end terminals are for fine stranded flexible cord and are not suitable for normal stranded cables.
OK - I'm going to ask you to defend that claim......
 
OK - I'm going to ask you to defend that claim......
Yikes!!! I'll go fetch my lawyer...
I guess I'm just basing this on personal experience. And the fact that the metal tube walls are much thinner on the cord end terminals (ferrules) than they are on the tubular crimps.
Could be wrong I guess...
Maybe we should get John Ward to conduct an experiment the results of which can be used as a legal precedent.
 
Never heard or seen that done before

I still use it a lot.

Whipping the end of a cable was more popular in the days before bootlace ferrules. Unlike using a ferrule, you can choose the diameter of the whipping wire to make the finished end the ideal size for the terminal. Like using a ferrule, it could theoretically increase contact resistance due to an extra layer of contact surface (cable contacts whipping, whipping contacts terminal) and some writers suggested this made it inherently bad practice. However the binding wire crossing the strands at right-angles creates a grid of point-contacts which is a pretty ideal scenario for both mechanical stability and low resistance.

Places you might still find it are small meter tails in normal meter cable entries, and older MEM EXELs and similar switchgear that have large terminals that do not clamp smaller cables effectively where some similar technique is required to make a satisfactory connection.
 
I have only ever done the wire-wrap style when soldering a couple of difficult wires together, so impressed to see it used for a cable clamp connection.

Certainly for 1.5mm-4mm conduit wire (7 strands) I frequently use ferrules as it reduces damage to the clamped end, more so for screw terminals on neutral/earth bars, etc.
 
....they're flattening or splatting more than I'd like..........
I wouldn't worry about the course strands flattening out in the cage clamp, the more the better as long as the clamp has a secure grip of the wire after all is done.

I didn't realise whip wrapping was still a thing, I haven't dressed a wire like that in 30 years... I assumed it was no longer considered good practice along with soldering.
 
Yikes!!! I'll go fetch my lawyer...
I guess I'm just basing this on personal experience. And the fact that the metal tube walls are much thinner on the cord end terminals (ferrules) than they are on the tubular crimps.
Could be wrong I guess...
Maybe we should get John Ward to conduct an experiment the results of which can be used as a legal precedent.
Sorry, poorly worded way of asking for your logic as to why!

I think the problem is less in a clamp, as all the strands can flatten and compress easily, it's in a large screw terminal with a smaller screw where if you lift the connection back out after you've screwed it in you see straight away that only the 'middle' has the imprint of the screw and a good 30% of the strands left and right of it have just been doing their own thing - and a ferrule will prevent that from happening.
 

Reply to To crimp or not? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi, Before I begin my tale of woe, I have my tin hat ready! I'm retired from the trade, I started out just as the 16th came in and had a rather...
Replies
35
Views
4K
Hello guys, I have a small problem assigning the correct codes for some visual faults. I am still confused and looking forward to find a good...
Replies
10
Views
5K
Hi. I am off grid, UK. There is no grid tie or connection and there is currently no potential for connection. Background: I use a Honda EU10i for...
Replies
0
Views
3K
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock