Discuss To re-wire? Or not to re-wire? in the UK Electrical Forum area at ElectriciansForums.net

EbolaSideRoom

-
Arms
Reaction score
104
Carried out an EICR in a domestic property today.
Client has recently purchased but not moved in, so place is empty. It's a detached bungalow, 2 beds, Gas-fired system boiler, detached garage.
There are 7 (yes 7) socket outlet circuits, all either B16A or B20A, each with no more than 6 outlets. R1 + R2 readings suggest spurs a-plenty, although the readings aren't outlandish. On the other hand, most of the IR readings come in sub 10 megohms, with two of the circuits having IR readings lower than 1 megohm L-E. There is only one lighting circuit, with 12 switches/points including the gas system boiler. Aside from a handful of C3 or FI codes (including the abovementioned IR readings) it is Satisfactory, yet I can't help feeling it wants rewiring, especially as it is empty for the time being.
Your thoughts?
 
Locate the faults and fix them....

Not sure I agree with your FI code for the low IR - I would state this as a C2

As for multiple socket radials - whats the problem with this?

How can you justify recommending a rewire ?
 
I presume from the word "client" that you are a professional spark who is offering his/her services to the general public? Why do you feel the need to ask basic questions on a forum? If you have done an EICR then you must have quite a bit of experience surely? Do you do this sort of work often??
 
It would be a good opportunity to update the wiring whilst the property is empty, especially if other renovation work is being carried out. But that doesn't mean it needs to be done.

Obviously the faults need repairing and perhaps it would be worth dividing the lighting on to two or more circuits, and maybe moving the boiler to one of the radial socket circuits.

Not sure what you mean about spurs a pleanty if the circuits are radial
 
What is your estimated age of the installation. Have you spoken to your client with regards as to the pros and cons and what they intend to do with the property, renting out may require just make good but if they intend to refurbish it then it may be beneficial to rewire to meet their needs. Either way the EICR should comment on it's current condition.
 
Locate the faults and fix them....

Not sure I agree with your FI code for the low IR - I would state this as a C2

As for multiple socket radials - whats the problem with this?

How can you justify recommending a rewire ?
IN reverse..
`I don't think that I can, it's just that it seems like it should be. I know that isn't really the correct approach, after all this is science, not art. This is why I'm asking. I haven't had the opportunity to discuss this with client yet either. TBH I'm inclined to agree with both your other comments; I have no problem at all with multiple socket radials (even if there are three different socket circuits in one room) and the low IR does speak of something going wrong in the near future.
 
IN reverse..
`I don't think that I can, it's just that it seems like it should be. I know that isn't really the correct approach, after all this is science, not art. This is why I'm asking. I haven't had the opportunity to discuss this with client yet either. TBH I'm inclined to agree with both your other comments; I have no problem at all with multiple socket radials (even if there are three different socket circuits in one room) and the low IR does speak of something going wrong in the near future.
Does the client live on another planet then? A 2 bedroom bungalow with 3 different socket circuits in one room??? Are you having a giggle?
 
It would be a good opportunity to update the wiring whilst the property is empty, especially if other renovation work is being carried out. But that doesn't mean it needs to be done.

Obviously the faults need repairing and perhaps it would be worth dividing the lighting on to two or more circuits, and maybe moving the boiler to one of the radial socket circuits.

Not sure what you mean about spurs a pleanty if the circuits are radial
That is my opinion really.
And by spurs a-plenty I'm suggesting that the radial circuits have been wired in branches, not linearly (is that a word?).
 

Reply to To re-wire? Or not to re-wire? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
The air conditioning on my Vauxhall Astra J has stopped working and I'm running out of ideas on how to fix it. Steps so far: The compressor clutch...
Replies
4
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
I have charged ahead with a small subpanel installation in a detached garage I am converting to a light-duty shop. The setup is simple, but I have...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock