Right Men, hear me out on this please.
I have a series of Rolec power pedestals with 2x 16 amp socket outlets on each one, each socket os protected by a C16 amp 30 mili amp double pole RCBO.
The supply cable is SWA and id inside an underground duct direct from the DB to the pillar, each pillar (there are two) has its own supply.
Now back at the DB each pillar is fed from a 32amp rcbo 30 mili amps instead of what I think should be just an MCB.
We all know that 100 miliamp time delay would be better at the Db to stop nuciance tripping which it does, and when I was doing RCD tests last week it was nigh impossible to keep my temper down with the rcbo at the board constantly tripping.
My question is does this installation need an RCBO at source when the cable is in a duct and completely protected.
Cannot quite see the reason.
Many thanks
Alexander.
 
The SWA if correctly installed is a cable with an earthed metallic covering so would not require 30mA RCD protection even if installed in a wall. As the cable is also in a duct there is no requirement for 30mA RCD protection.
As Telectrix states only if the installation at the DB is a TT system, without an ultra low Ra, would an RCD for fault protection be required, in that case the rating of the RCD would need to be low enough to operate with the existing Ra value and because of the 30mA RCBOs at the final circuits the RCD would need to be selective to allow discrimination.
The existing arrangement is not too bad from a compliance point of view because each RCD is protecting the same circuit so there is no nuisance tripping whichever one goes, but as you say the testing is a real nuisance.
 

Reply to To use an RCBO or not to use an RCBO . in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Gents. I did some earth loop tests on Rolec power pedestals (2x 16 amp outlets) that are harbour side, looped in and out from one another. Three...
Replies
7
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi, I’m after some advice for an existing car charger that’s on one of our newly inherited sites. We have a Rolec 2x 7.2kw pedestal charger, just...
Replies
0
Views
1K
The bit where I cut to the chase is in bold below if you can't be bothered with the back story. Changing MCB in main house DB for garage supply...
Replies
9
Views
4K
  • Locked
Have still not installed my Neff induction hob but is near. Was originally going to use 3phase but got battered on here so no. I have a 3 phase...
Replies
19
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock