Right Men, hear me out on this please.
I have a series of Rolec power pedestals with 2x 16 amp socket outlets on each one, each socket os protected by a C16 amp 30 mili amp double pole RCBO.
The supply cable is SWA and id inside an underground duct direct from the DB to the pillar, each pillar (there are two) has its own supply.
Now back at the DB each pillar is fed from a 32amp rcbo 30 mili amps instead of what I think should be just an MCB.
We all know that 100 miliamp time delay would be better at the Db to stop nuciance tripping which it does, and when I was doing RCD tests last week it was nigh impossible to keep my temper down with the rcbo at the board constantly tripping.
My question is does this installation need an RCBO at source when the cable is in a duct and completely protected.
Cannot quite see the reason.
Many thanks
Alexander.
I have a series of Rolec power pedestals with 2x 16 amp socket outlets on each one, each socket os protected by a C16 amp 30 mili amp double pole RCBO.
The supply cable is SWA and id inside an underground duct direct from the DB to the pillar, each pillar (there are two) has its own supply.
Now back at the DB each pillar is fed from a 32amp rcbo 30 mili amps instead of what I think should be just an MCB.
We all know that 100 miliamp time delay would be better at the Db to stop nuciance tripping which it does, and when I was doing RCD tests last week it was nigh impossible to keep my temper down with the rcbo at the board constantly tripping.
My question is does this installation need an RCBO at source when the cable is in a duct and completely protected.
Cannot quite see the reason.
Many thanks
Alexander.