Steel instead of copper in the t&e, I know now I probably should have tested first and to be honest I agreed to do the job as a favour for a friend and I'm starting to regret it, and yes I am an electrician I have spent my seven years on new build schools so my domestic fault finding ability is non existent.
 
Fault finding in cables is fault finding in cables no matter where you carry it out mate, a methodical approach is all thats needed.
Steel T&E is something I have never seen in 29 years since I qualified, are you absolutely sure about that?
Once again, what test results did you get from your RFCs?
 
@ OP. try a magnet on the cable. bet it's tinned copper or alli. then you need to IR test each circuit, check for crossed/shared neutrals. and most important, make sure you've not crossed neutrals into wron bar in CU and check manufacturers tails. they have been known to be wired wrong in the sweat shop. (sorry, far eastern technology factory)
 
Just out of interest Sam, what tests did you carry out during your CU change? Have you notified it? What certification did you issue?
What tester are you using?
 
RCD tripped. narrowed down to SWA feeding hot tub. never seen SWA connected like this before. armour not earthed anywhere. was supposedly professionally installed. the pic shows a 30mA plug-in power breaker RCD, the type you'd fit to a lawn mower cable!

View attachment 12828

disconnected both ends and IR tested SWA . L/E 0.04 Meg. N/E 0.23 Meg. 40m of SWA, partly buried. half way down had been repaired? with choc block and tape.

so , it's quote for new SWA, glands, ad. box, correct installation. what i'm not happy with is that it's fed from the garage sub-main which is in turn fed from the house RCD in a split board, so a fault will take out all in the house except lighting. now, i've not done any work on hot tubs, but my thinking is to feed the garage sub. from the non protected side of the house ( it's fed in SWA ) and then fit RCBO in the sub. to cover the garage socket ( just a fridge/freezer) and a 13A FCU to feed the SWA to the hot tub. anyone see a flaw in this? worked out the VD at 13A to be 9.5V using 40m of 2.5mm SWA.

13A sounds a bit low for a hot tub all the tubs I've worked on have been 20A - 30A supply to cope with the heater(s) and the pumps. Have you checked the supply requirements of the tub as given the poor original install I would not take anything for granted
 
thought that at first, but it has been running on a 13A 1362 quite happily before the cable failed.
 
RCD tripped. narrowed down to SWA feeding hot tub. never seen SWA connected like this before. armour not earthed anywhere. was supposedly professionally installed. the pic shows a 30mA plug-in power breaker RCD, the type you'd fit to a lawn mower cable!

View attachment 12828

disconnected both ends and IR tested SWA . L/E 0.04 Meg. N/E 0.23 Meg. 40m of SWA, partly buried. half way down had been repaired? with choc block and tape.

so , it's quote for new SWA, glands, ad. box, correct installation. what i'm not happy with is that it's fed from the garage sub-main which is in turn fed from the house RCD in a split board, so a fault will take out all in the house except lighting. now, i've not done any work on hot tubs, but my thinking is to feed the garage sub. from the non protected side of the house ( it's fed in SWA ) and then fit RCBO in the sub. to cover the garage socket ( just a fridge/freezer) and a 13A FCU to feed the SWA to the hot tub. anyone see a flaw in this? worked out the VD at 13A to be 9.5V using 40m of 2.5mm SWA.


Hi Telectrix,

I wired a hot tub not too long ago and went by the supplier spec.
They requested a C type 20A mcb, due to start up surge. Also, i wired the supply from the C type mcb in 2.5 swa, into an isolator which also had a commando socket outlet. The company then hooked up the hot tub from their end into the commando socket.

If you do put an RCBO, make sure its C type, as you may have problems on start up.

Hope this helps,
Sav
 

Reply to today's fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
782
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock