I dont know if you looked at this post Tel.

hot tubs

just read through it. at the end of the day, my remit is to replace a damaged SWA. but in the process, comply with current regs. and make as safe as possible. also , i'm not happy with the supply being fed from the 1 RCD in the split board in the house, as a fault on the hot tub or in the garage will knock out all the house socket circuits. i need a closer look at the tub ( rating, mounting, any extraneous parts, etc., before finalizing the job.
 
funny, was just thinking about earthing arrangement. it's TNC-S and the hot tub is mounted on wooden decking. from what i saw , there is no integral RCD protection. that came from the plug-on power breaker in the pic. would you recommend using the PME earthing ( as it was ) but banging in a rod at the hot tub as well?

i've read through section 702 as being the nearest reg. reference ( swimming pools and other basins) . can't find any reference in the bgb to hot tubs per se.
Any chance of getting the manuf instructions Tel? They often stipulate installing a rod at the tub end.
 
no instructions. client inherited tub when they bought the house. as i said earlier, it was bucketing down yestrday, so will have to go back and check rating etc., but as it has been running in a 13A plug-in for the last 7 years or so, i am working on the basis that it's no more than 3kW.
 
Sorry i got it wrong, it was GN7 that was being quoted!! lol!!
But even here, it's still not clear what rules/reg's an external hot tub/jacuzzi fall under.... Taking a wild stab, i'd say they have more in common with an outdoor swimming pool than other basin's... lol!!

quote_icon.png
Originally Posted by spark 68
Just out of interest, what does a Jaccuzi fall under ?, would it be under swimming pools and other basins ?, or just under normal bathroom regs ?

A look though GN7 suggests you can use PME for swimming pools and other basins (Zone 2), but with a requirement to have an earthmat or earth electrode 20 ohms or less to be installed and connected to the protective equipotential conductor. 702.410.3.4.3


As far as manufacturers instructions go, you could always try the companies website, they may just have PDF files for their equipment. Or even contact them direct for guidance...



 
Well...yes, someone comes here politely asking for a bit of advice and gets bombarded with interrogation and accusations by the usual do gooder, electrical police types. Why should someone who's only ever worked on new builds know what cable was made out of in the 50's. Its not as if they teach it at college.

He might have been working on new builds for a long time. Does'nt seem like it though.
Anyone who thinks we were ever using steel as a cable conductor in house wiring has to come under a great deal of suspicion. May be polite, may also be very inexperienced.

Basics:mickey:
 
He might have been working on new builds for a long time. Does'nt seem like it though.
Anyone who thinks we were ever using steel as a cable conductor in house wiring has to come under a great deal of suspicion. May be polite, may also be very inexperienced.

Basics:mickey:

I was thinking the same myself
 

Reply to today's fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
782
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock