Hi,

New to the forum and I've got an issue in my house. I''mnot an electrician.

Our main RCD tripped last night and after investigating I've found the cause to be one of the sockets in the living room.
Testing the socket shows 50v across L+N, 230v across L+E, 30V across N+E.
Am I right in assuming there is a missing neutral connection?

The socket appears to be spurred off as there's only a single cable.
Maybe a junction box underneath the floor as I can't see where it's spurred from looking at the other sockets :(

Will I need to take my floor up?
 
You need to ring someone to be fair fella to test the circuit with an instrument suitable for the job, it could be several things, but a loose Neutral is one possibility.
 
Best advice Martin would be call an Electrician, as you say you are not an Electrician, playing about with this problem could be costly as you probably don't or won't know what you are looking for, could be a simple job but you won't know until a sparky looks at the problem, post your exact location one of the Members local to you may offer assistance.
 
Judging by the avatars Tel I'm the old fart, right you just wait mate.
i know you can take the banter, pete. you give enough out - like me. you know it's all in jest. no time for these prima donnas who can't take a joke. Up the Old Gits .
upload_2018-9-5_20-23-49.jpeg
 
The RCD tripping could be a a complete coincidence with you finding this socket .
Yep. It may have been like that for a while.
It may be leakage somewhere else causing the trip.
Get someone in to investigate, generally.
…...an old git rather than a prima donna, maybe?
 
To be honest it's been around 2 years since we've last used that socket. So could be coincidence
I'm Stockton-on-Tees area.

I'm not fussed about it working as we don't use it, or should it be fixed to remove any potential issues.
 
:D
Yeah but the OP needs a spark :D

Ah go boil yer heid!


I'm Stockton-on-Tees area.

Too far for me, mate. Sorry.

I'm not fussed about it working as we don't use it, or should it be fixed to remove any potential issues.

It should be fixed.
If you have a loose connection somewhere there could be arcing... continuing heat damage to cables and a possibility of a fire.
Sorry to be the profit of doom.
 
It should be fixed.
If you have a loose connection somewhere there could be arcing... continuing heat damage to cables and a possibility of a fire.
Sorry to be the profit of doom.[/QUOTE]


You after making a quick buck, or what?
 
Yeah, a circuit that has a fault should either be isolated (completely disconnected) or repaired for safety. Faulty circuits that are left live can cause equipment damage, electric shock, inconvenient RCD tripping faults and even fires.
 

Reply to Tripped Socket - 50v in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
753
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
485
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
479
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
290
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock