Discuss Trying to install TCP wifi switch. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I recently bought a TCP wifi switch and tried to install it my self.
Behind my room light switch i have 2 red and 1 one black wire.
I tried putting one red in lin, one red in load 1 and black in N but unable to switch the switch on.

i have tried every possible combination the wire might go but unable to switch it on.
I tried plugging 2 red together in Lin and Black in N, the light stayed on but the blue light on switch didnt come on.

please can anyone assist me on which wire goes where as none of the electricians i know arent willing to help.
95DA585B-B84B-420C-9A20-0B19697409A4.jpeg
 
it's possible that you do not have a N at the switch position. a pic. of how the original switch was wired would help.
 
as i see it, youneed the live feed in Lin, the switch wire to light in Load, then light will work. however, it seems you need a N in the 3rd terminal to enable the switch blue light to work. have you got a pic. of the instructions wiring diagram?
 
as i see it, youneed the live feed in Lin, the switch wire to light in Load, then light will work. however, it seems you need a N in the 3rd terminal to enable the switch blue light to work. have you got a pic. of the instructions wiring diagram?
There were no instructions in the box as it only said attach the switch and download the app but i managed to find a diagram online as attached.
 

Attachments

  • CA2434EF-7BAF-4A5D-861A-960E067F67E8.png
    214.2 KB · Views: 46
Unfortunately, you need a neutral for the switch to work correctly.
Do you have a picture of where the wires went in the old switch?
 
There were no instructions in the box as it only said attach the switch and download the app but i managed to find a diagram online as attached.
Had to take the picture without my mrs knowing as I ruined the wall yesterday. ??
[automerge]1599653258[/automerge]
Unfortunately, you need a neutral for the switch to work correctly.
Do you have a picture of where the wires went in the old switch?
Hi James,
Thanks for the reply, please see attached picture of the old and new switch.
 

Attachments

  • 49874FFB-F55A-4F83-BAE6-8D717E3E7FD9.jpeg
    150.5 KB · Views: 46
  • 962C9A62-241A-467E-AFC2-2CFE63AB469F.jpeg
    67.9 KB · Views: 39
the old switch is 2 way, so there's another switch for the light elsewhere. to make it work properly would require some re wiring of the switches to lights. if you get the switch working with existing wiring config. thast's a bonus, but you'll never get the switch illumination without providing a neutral at the switch.
 
The WiFi switch requires a neutral to power its internal electronics. The black wire at your original switch appears to be a 2-way strapper, not a neutral, therefore the switch cannot work with your existing wiring as it is. Whether it can be rejigged without chasing out your walls to add a cable, or whether you will have to replace the switch with a type that does not require a neutral and possibly add a dummy load to power it, will depend on exactly how the cables have been run and what lights it feeds.

In any event, I would advise against trying random combinations of wires when you don't know what is going on. Product damage and personal injury can result, also fireballs and other unspecified apocalypses.
 
the old switch is 2 way, so there's another switch for the light elsewhere. to make it work properly would require some re wiring of the switches to lights. if you get the switch working with existing wiring config. thast's a bonus, but you'll never get the switch illumination without providing a neutral at the switch.
Thanks for your assistance.
[automerge]1600641730[/automerge]
The WiFi switch requires a neutral to power its internal electronics. The black wire at your original switch appears to be a 2-way strapper, not a neutral, therefore the switch cannot work with your existing wiring as it is. Whether it can be rejigged without chasing out your walls to add a cable, or whether you will have to replace the switch with a type that does not require a neutral and possibly add a dummy load to power it, will depend on exactly how the cables have been run and what lights it feeds.

In any event, I would advise against trying random combinations of wires when you don't know what is going on. Product damage and personal injury can result, also fireballs and other unspecified apocalypses.
Thanks, ill consult with an electrician and what they can do.
 
If this 1W switch is wired conventionally, replacing the T&E cable between the light rose and the switch with 3&E will enable you to feed the neutral to the switch.
You might also have a problem with the depth of that back box. Might be wrong, but it looks like 16mm, rather than 25 or 35mm deep.
 
If this 1W switch is wired conventionally, replacing the T&E cable between the light rose and the switch with 3&E will enable you to feed the neutral to the switch.
You might also have a problem with the depth of that back box. Might be wrong, but it looks like 16mm, rather than 25 or 35mm deep.
Yes i hav it at 35mm now but it seems now the wires are the issue i never thought of
 

Reply to Trying to install TCP wifi switch. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
321
Is the following set up possible with a 3 Gang 2 Way Smart Wifi Switch set up (the black glass type touch ones) One of the 3 switches, switches...
Replies
2
Views
527
Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
466
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
212
FYI --- This is a U.S. installation. I'm replacing a three way switch (the UK might more sensibly call it a two way switch??) with a Kasa Smart...
Replies
4
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock