Hi folks, I have issues with a job I was on today with an outside metal enclosure being bonded from a tns system and right next to it I have another metal enclosure which is bonded thought an earth pit and tt system as there are supplies to caravans protected by the tt system. My issue is the fact 2 different earthing systems are simultaneously touchable and could have different potentials, what's everyone's take on this ? Thanks
 
I would question why the caravan supplies aren't on the TNS supply?

You're right that this is not a good situation as you have two separate earth potentials in close proximity
 
I would guess that work was carried out, earthing was previously via armour of swa back to intake origin, which has since deteriorated and giving an unacceptably high efli, so they've gone TT to bypass the existing tns.

Well at least that's what I've seen contractors do before on these places when I worked on them
 
If the supply origin is common then Rod the TNS as well as leaving its earthing as is, if they come off different origins then this increases the risk of a PD between the 2 earthing set-ups.
 
Last edited:
I would guess that work was carried out, earthing was previously via armour of swa back to intake origin, which has since deteriorated and giving an unacceptably high efli, so they've gone TT to bypass the existing tns.

Well at least that's what I've seen contractors do before on these places when I worked on them

Which is not compliant, if the SWA has deteriorated then it is unfit for continued service and should be replaced.
 
Not exactly sure why they haven't used the tns Earth, but yeah it is swa into enclosure 1 with the tns protection then a supply from enclosure 1 to the 2nd enclosure where the caravan supplies are fed from with the Earth pit adjacent.

any thoughts of a code on a condition report for this am Thinking code 2 ?
 

Reply to Tt and tns sytem together in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi How do i access the earth rod to service it, where abouts will it be located and does a tt system have upfront rcds which will be probably in...
Replies
3
Views
985
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
623
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
541
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
567

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock