W

Welchyboy

HI all anyone know the above, i put 1667 ohms in the box normally for all TT circuits but noticed the other day it is only for circuits upto 32A

Anyone enlighten me, i need it for a 50A and 40A circuit??

thanks
 
Hi,
The 1667 ohms refers to the max ZS for a 30mA RCD to meet the disconnection time, but over 200 ohms may be unstable.

BTW, I use the BS7671 certs from the IET site, and I cannot see where to put the max ZS ie. 1667 ohms for TT on this cert. I usually just put my measured/calculated results on the schedule of test results for each particular circuit, and obviously the measured ZE/RA on the relevent sheet.
 
Last edited:
Regulation 411.3.2.4 applies with TT type earthing systems for distribution circuits (and circuits over 32A). Disconnection time is not allowed to exceed 1 second for the protective device. I can't imagine why you would allow a higher max Zs than 1667Ohms, as it's purpose is to ensure disconnection before the PD reaches 50V, unless I'm missing something.
 
Just grabbed the BRB (BGB on order) and 411.5.4 would also apply without an RCD ... ie Zs x Ia <= U0 must be satisfied ... which would give:

for 40A) Zs x 40A <= 230 which would give Zs as max 5.75 Ohms
for 50A) Zs x 50A <= 230 which would give Zs as max 4.6 Ohms

You must also meet the disconnection time of 1S.
 
TT systems: 411.5.3 (p50)
Where an RCD is used for earth fault protection, the following conditions shall be fulfilled:
(i) the dissconection time shall be that required by regulation 411.3.2.2 or 411.3.2.4 and
(ii) Ra x I delta n< 50V
As topquark...
 
With TT circuits, all circuits must be protected by an RCD as TQ said, regardless of the size of the over current protection device.

The max ZS refers to the trip current rating of the RCD, again as TQ said to prevent the PD rising above 50V (touch voltage).

30mA = 1667 ohms
100mA = 500 ohms
300mA = 167 ohms
500mA = 100 ohms

these are the absolute max values, and in practice we should aim to be as low as possible.

Ps. in some special locations the touch voltage may be limited to <= 25V, and these require an even lower max ZS and/or RA

Sorry to confuse, the joys of forum posting
 
Last edited:
With TT circuits, all circuits must be protected by an RCD as TQ said, regardless of the size of the over current protection device.

The max ZS refers to the trip current rating of the RCD, again as TQ said to prevent the PD rising above 50V (touch voltage).

30mA = 1667 ohms
100mA = 500 ohms
300mA = 167 ohms
500mA = 100 ohms

these are the absolute max values, and in practice we should aim to be as low as possible.
Did I say that? ;)
 
To be fair there is no rule that says that all circuits have to be. It's just difficult to get Ze(Ra) low enough to get the Zs low enough to comply without an RCD. Keep in mind distribution circuits may not want to be RCD protected at source, unless using a slower trip to get some discrimination.
 
To be fair there is no rule that says that all circuits have to be. It's just difficult to get Ze(Ra) low enough to get the Zs low enough to comply without an RCD. Keep in mind distribution circuits may not want to be RCD protected at source, unless using a slower trip to get some discrimination.
Well that was the idea behind 100mA time delayed`s wasn`t it?..........
 
With TT circuits, all circuits must be protected by an RCD as TQ said, regardless of the size of the over current protection device.

The max ZS refers to the trip current rating of the RCD, again as TQ said to prevent the PD rising above 50V (touch voltage).

30mA = 1667 ohms
100mA = 500 ohms
300mA = 167 ohms
500mA = 100 ohms

these are the absolute max values, and in practice we should aim to be as low as possible.

Ps. in some special locations the touch voltage may be limited to <= 25V, and these require an even lower max ZS and/or RA
Sorry to confuse, the joys of forum posting

I don't think you'll find a 25V touch voltage stipulated anywhere in BS7671:2008
 
I don't think you'll find a 25V touch voltage stipulated anywhere in BS7671:2008

To be honest I cannot remember where I came across a 25V touch voltage, it may have been when I did a stint panel building/assisting in testing, possibly a panel for the gas/petroleum industry or medical ?, I had it in my mind possibly for swimming pools, but a quick look at the regs suggests otherwise.:smile5:
 
Last edited:

Reply to TT Max ZS loop reading for circuits over 32A in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
389
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock