Have recently been on an industrial job where a 3 phase 200A supply is distributed as a TT network between DB's in 1 large building and subbed out to others via 5 core cables, ie The cpc is continuous throughout.There are stakes at the origin and at all db's outside the eq zone.There is an S type rcd at the origin and another at the main panel that appear to discriminate.No further Rcd's other than RCBO's in local boards to give 30ma protection to sockets etc that require additional protection.It was wired to the 17th.Am aware of the need for each cpc to be able to carry all fault currents but what do people think of this set up? overall Ze with everything connected is as low as 5 ohms. comments appreciated. could work out a schematic if anyone is interested.
 
That sounds like a typical industrial TT system to me John. Some S type RCDs have adjustable elements and others are time set. I'm surprised that the 5 ohm Ra isn't lower, if all of the several stakes have been linked out...
 
Thanks for that, my experience of TT in an industrial setting is limited so advice is appreciated.
Another query about the same install then....
My MFT (Dilog) on performing an Earth loop gives 2 results: Earth fault loop impedance & Line loop impedance . In this case clearly The line loop is much lower..question is which value to record as Zs when measuring for final circuits? my colleague has Megger MFT and this only gives the lower reading.Amtech doesnt like this as it exceeds the auto filled max Zs for the device.In this case should one record the max Zs for the nearest upstream RCD ie 1667ohms or whatever and the earth fault loop for the overcurrent device max Zs and the lower figure from the tester? If the former is the case how would my colleague get on not having the true earth loop from his Megger?
 
Last edited:

Reply to TT network in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all,looking for some pointers to an RCD problem, I work entirely on large poultry farms, I've only been in post a year, at some point before I...
Replies
6
Views
2K
Pme Swa sub main supplying external tennis courts. Because of cable size,tt system will be installed. The original Pme supply comes from main...
Replies
14
Views
3K
....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
Replies
29
Views
4K
Been to a job today, rewire Immersion cct to suit new cylinder pos. Did Zs got 12 ohm....looked a little closer... Immersion fed from b16 breaker...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock