Hi there
Just a little advice required on RCD testing:
I did some Minor Works the other day and obtained thefollowing RCD test readings –
TT system
100amp 30mA RCD protecting the CCU.
Circuit tested was a 32a ring final circuit with 32aovercurrent protection MCB type b.
0 degress
X 0.5 = no trip
X 1 = 29.5ms
X 5 = 9ms

180 degrees
X 0.5 = no trip
X 1 = 18ms
X 5 = 16ms

I was expecting similar readings on the 180 degree test compared to the0 degrees test. Can someone shed any light on the difference between the 0& 180 degree test and whether these readings look normal?.

I assumed the difference is the stage of the waveform the test is takenat?.

Overall ELI at the socket under test was 29.5 ohms

Also I noticed the Main Earth to the installation is 10mm, although thecable is buried without mechanical protection?, having looked at table 54.1(p159) it would appear the cable should be 16mm. I assume even though the ELIis ok the cable should really be replaced?.

Your thoughts and advice would be appreciated

Regards
Smart Sparks
 
As P&S ^^^ above,

This is perfectly normal and are typical readings, the way I understand it is that some RCD's are more sensitive on one half cycle than the other, maybe be some other posters can confirm this, or expand on the reasons why.
 
As P&S ^^^ above,

This is perfectly normal and are typical readings, the way I understand it is that some RCD's are more sensitive on one half cycle than the other, maybe be some other posters can confirm this, or expand on the reasons why.

That's it exactly :)
 
As all of the above. Repeat the tests 10 times and you will get 10 different results. It complies with 415.1.1 Job done.

Cheers.........Howard
 
main earthing conductor on a TTsystem is minimum 6mm if not mechanically protected. no need for 16mm
 
Thanks for the feedback.

It is possible something was plugged in, i assume that can have an effect then.

I feel better now i know the resuits sound ok. i am a little confused on the earth size as the table in the regs states 16mm in table 54.1. Just out of interest where does the 6mm come from?.
 
Thanks for the feedback.

It is possible something was plugged in, i assume that can have an effect then.

I feel better now i know the resuits sound ok. i am a little confused on the earth size as the table in the regs states 16mm in table 54.1. Just out of interest where does the 6mm come from?.

I believe the minimum size is 16mm buried without mechanical protection.
 
my bad. missed the "buried". most read post fully before replying.:disguise:
 
By definition, AC current comprises of positive and negative half cycles with respect to a zero reference point, and an AC fault current can start to flow to earth at any point during either half cycle. An AC Type RCD will only trip in response to either the positive or negative half cycles of the AC earth fault current, whereas an A Type RCD will respond to both half cycles. As the AC Type RCD is blind to either the positive or negative half cycles of an AC fault current, the fault current could flow for up to 10mS before the RCD will see the fault current. This 10mS will be added to the response time of the device.
RCD testers are usually provided with a switch to enable the user to start the flow of the test current at 0 degrees or 180 degrees, i.e. starting on a positive going or a negative going half cycle respectively. By starting the testing of the RCD at both settings of the test current conduction angle, the user will be able to determine the maximum trip time of the RCD. This can be done at different test current levels.
 
By definition, AC current comprises of positive and negative half cycles with respect to a zero reference point, and an AC fault current can start to flow to earth at any point during either half cycle. An AC Type RCD will only trip in response to either the positive or negative half cycles of the AC earth fault current, whereas an A Type RCD will respond to both half cycles. As the AC Type RCD is blind to either the positive or negative half cycles of an AC fault current, the fault current could flow for up to 10mS before the RCD will see the fault current. This 10mS will be added to the response time of the device.
RCD testers are usually provided with a switch to enable the user to start the flow of the test current at 0 degrees or 180 degrees, i.e. starting on a positive going or a negative going half cycle respectively. By starting the testing of the RCD at both settings of the test current conduction angle, the user will be able to determine the maximum trip time of the RCD. This can be done at different test current levels.

The above description of RCD types is in my view misleading and in part wrong.

[FONT=&amp] Semi-conductor devices are now incorporated in equipment used throughout industry, commerce and in the home. Typically, the purpose of these semiconductor devices is for monitoring and controlling industrial equipment e.g. speed controls for small motors and temperature controls, along with extensive use in computer equipment and household appliances e.t.c. As the equipment is fed from the mains electrical supply, in the event of an earth fault the presence of semi-conductors may result in the normal ac waveform being replaced by a non-sinusoidal fault current. In some cases the waveform may be rectified or chopped. These waveforms are said to contain a pulsating dc component which can either partially de-sensitise or totally disable a standard Type AC RCD.[/FONT] Because of this phenomenon Type A RCDs [FONT=&amp]were introduced, [/FONT]where tripping is assured[FONT=&amp] for residual sinusoidal alternating currents and residual pulsating direct currents, whether suddenly applied or slowly arising.[/FONT]
 
Last edited by a moderator:
The above description of RCD types is in my view misleading and in part wrong.

[FONT=&amp] Semi-conductor devices are now incorporated in equipment used throughout industry, commerce and in the home. Typically, the purpose of these semiconductor devices is for monitoring and controlling industrial equipment e.g. speed controls for small motors and temperature controls, along with extensive use in computer equipment and household appliances e.t.c. As the equipment is fed from the mains electrical supply, in the event of an earth fault the presence of semi-conductors may result in the normal ac waveform being replaced by a non-sinusoidal fault current. In some cases the waveform may be rectified or chopped. These waveforms are said to contain a pulsating dc component which can either partially de-sensitise or totally disable a standard Type AC RCD.[/FONT] Because of this phenomenon Type A RCDs [FONT=&amp]were introduced, [/FONT]where tripping is assured[FONT=&amp] for residual sinusoidal alternating currents and residual pulsating direct currents, whether suddenly applied or slowly arising.[/FONT]
in other words, a bit of electronic trickery.
 

Reply to TT / RCD testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I'd like some information on the RCD test features and process please. Firstly, does this only apply to sockets or lighting circuits too? Clearly...
Replies
11
Views
1K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Having a bit of a brain freeze moment. I have a 2-core SWA cable running to an outbuilding. The sheath is used to earth this cable back to the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock