Hi there
Just a little advice required on RCD testing:
I did some Minor Works the other day and obtained thefollowing RCD test readings –
TT system
100amp 30mA RCD protecting the CCU.
Circuit tested was a 32a ring final circuit with 32aovercurrent protection MCB type b.
0 degress
X 0.5 = no trip
X 1 = 29.5ms
X 5 = 9ms

180 degrees
X 0.5 = no trip
X 1 = 18ms
X 5 = 16ms

I was expecting similar readings on the 180 degree test compared to the0 degrees test. Can someone shed any light on the difference between the 0& 180 degree test and whether these readings look normal?.

I assumed the difference is the stage of the waveform the test is takenat?.

Overall ELI at the socket under test was 29.5 ohms

Also I noticed the Main Earth to the installation is 10mm, although thecable is buried without mechanical protection?, having looked at table 54.1(p159) it would appear the cable should be 16mm. I assume even though the ELIis ok the cable should really be replaced?.

Your thoughts and advice would be appreciated

Regards
Smart Sparks
 
As P&S ^^^ above,

This is perfectly normal and are typical readings, the way I understand it is that some RCD's are more sensitive on one half cycle than the other, maybe be some other posters can confirm this, or expand on the reasons why.
 
As P&S ^^^ above,

This is perfectly normal and are typical readings, the way I understand it is that some RCD's are more sensitive on one half cycle than the other, maybe be some other posters can confirm this, or expand on the reasons why.

That's it exactly :)
 
As all of the above. Repeat the tests 10 times and you will get 10 different results. It complies with 415.1.1 Job done.

Cheers.........Howard
 
main earthing conductor on a TTsystem is minimum 6mm if not mechanically protected. no need for 16mm
 
Thanks for the feedback.

It is possible something was plugged in, i assume that can have an effect then.

I feel better now i know the resuits sound ok. i am a little confused on the earth size as the table in the regs states 16mm in table 54.1. Just out of interest where does the 6mm come from?.
 
Thanks for the feedback.

It is possible something was plugged in, i assume that can have an effect then.

I feel better now i know the resuits sound ok. i am a little confused on the earth size as the table in the regs states 16mm in table 54.1. Just out of interest where does the 6mm come from?.

I believe the minimum size is 16mm buried without mechanical protection.
 
my bad. missed the "buried". most read post fully before replying.:disguise:
 

Reply to TT / RCD testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I'd like some information on the RCD test features and process please. Firstly, does this only apply to sockets or lighting circuits too? Clearly...
Replies
11
Views
1K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Having a bit of a brain freeze moment. I have a 2-core SWA cable running to an outbuilding. The sheath is used to earth this cable back to the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock