I have a couple of questions regarding a TT installation:

1) can overhead twin and earth submain supplying a house (on catenary wire) be protected by a 100mA time delay
rcd then 2x 30mA split load in house. (as meter position /swtich fuse) is in a seperate shed/building. or does it depend on what earth fault loop impedance i get form the earth rod (next to meter)? If so, how do i calculate?

2) in a farm building, can a submain be covered by 100 mA time delay if the twin and earth is enclosed in pvc conduit up the wall then clipped direct up in the roof then dropped in conduit (not likely to get damaged in roof as its very high). and then use 30mA for the final circuits. It is assumed no livestock is being kept in this building, but would that make a difference? (this is TT installation again)

thank you
any advice is great
 
1)no i would not say twin and earth is the best for an overhead - but this is existing and may have been installed correctly at the time of its regs. I have worked alot on National Trust properties and you find these alot. Perhaps you just work new installations mostly? Done many condition reports containing overhead cables - Advised by NIC inspectors - they are acceptable , providing they are supported correctly and of a suitable height etc . i just was unsure on rcd protection of them? Obviously swa would be first choice to install! If i protect it by a 30mA RCD then it gives no discrimination within the house - unless i provide a time delay 30mA for the submain but you don't see many of these around

2) Many agricultural installatons i have seen have t&e clipped direct in roofs and piped down on drops - i would just like some advice on rcd protection. If a twin and cable is installed in a roof above the height and out of reach from livestock etc surely this is the same as clipping a cable direct in an open ceiling/open beams of a nineteen hundreds' pub where mechanical protection is not required

i appreciate your answers but would also like some practical advice - thank you
 
Uv degradation for a start on Q1
Mechanical damage from rodents alone on Q2
I have been in more than my fair share of spit and sawdust back water establishments in my younger days as a young farmer , but even those ( I hope ) were generally rodent free !:puke:
I would have thought an S type 30mA rcd sort of defeats the object of installing it in the first place !? Hence their rarity ?
 
1)no i would not say twin and earth is the best for an overhead - but this is existing and may have been installed correctly at the time of its regs. I have worked alot on National Trust properties and you find these alot. Perhaps you just work new installations mostly? Done many condition reports containing overhead cables - Advised by NIC inspectors - they are acceptable , providing they are supported correctly and of a suitable height etc . i just was unsure on rcd protection of them? Obviously swa would be first choice to install! If i protect it by a 30mA RCD then it gives no discrimination within the house - unless i provide a time delay 30mA for the submain but you don't see many of these around

2) Many agricultural installatons i have seen have t&e clipped direct in roofs and piped down on drops - i would just like some advice on rcd protection. If a twin and cable is installed in a roof above the height and out of reach from livestock etc surely this is the same as clipping a cable direct in an open ceiling/open beams of a nineteen hundreds' pub where mechanical protection is not required

i appreciate your answers but would also like some practical advice - thank you

If you have done a lot of work on installations of this type how come the question of RCD's has only just become an issue
 

Reply to TT Submains RCD question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
875
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
863
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock