ok, first things first, happy new year to all members
now on to the problem,
i live in a rented house and my landlord has asked me to do some remedial work for him after a recent report came back as unsatisfactory.
1 of the 'snags' was that the db which is installed in a tt system has only 1 rcd? this is 30mA the tester gave it a 4 grade on the test sheet which means non-compliant with the regs but i dont have a copy handy. I have yet to do my 17th but dont remember it on the 16th and have seen hundreds of them fitted like this when i was younger working for a housing company. Are you supposed to fit a 100mA rcd at primary source?
thanks guys
matt
now on to the problem,
i live in a rented house and my landlord has asked me to do some remedial work for him after a recent report came back as unsatisfactory.
1 of the 'snags' was that the db which is installed in a tt system has only 1 rcd? this is 30mA the tester gave it a 4 grade on the test sheet which means non-compliant with the regs but i dont have a copy handy. I have yet to do my 17th but dont remember it on the 16th and have seen hundreds of them fitted like this when i was younger working for a housing company. Are you supposed to fit a 100mA rcd at primary source?