Hi all,

Doing an EICR on a property which is 3Ph in and then 3 x Single phase boards from that. However it's on a TT System and doesn't have a upfront 100mA RCD and I am not aware of any reason why one wouldn't be required.

So I am just wondering if this MCG one will suffice into an enclosure.


Or if I need to go balls to the wall and get this Hager one


Obviously I need to justify to the client the cost difference and brand name I know Hager is great kit. But if anyone has any other recommendations it would be appreciated.
 
The MCG one appears to be time delayed type AC, hager seems to be non time delayed type A

I'd want to fit a time delayed type A really, but you also need to be sure the down stream boards have non time delayed rcds upfront, or rcbos with switched neutral
Good spot on the non-time delay. Never noticed that at first after I got sidetracked at the price. 😂

The downstream boards are 2 x Hager split load dual 30mA RCD

The third board is a fuse box RCBO board
 
Last edited:
Good spot on the non-time delay. Never noticed that at first after I got sidetracked at the price. 😂

The downstream boards are 2 x Hager split loaf dual 30mA RCD

The third board is a fuse box RCBO board

Ok, so you need to make sure those fusebox rcbos are switched neutral, if not, in the event of a N-E fault the neutral will still remain in circuit after the rcbo has tripped, likely taking out the big boy upfront
 
Ok, so you need to make sure those fusebox rcbos are switched neutral, if not, in the event of a N-E fault the neutral will still remain in circuit after the rcbo has tripped, likely taking out the big boy upfront

All fusebox RCBOs are now switched neutral. I don't think they make any other kind now.
 
The miniature ones are AFAIK, don't know about the full height ones though.
The full height are too.
IMG_0002.jpeg
 
I am right is thinking it has to be a time delayed RCD upfront and not just a 100mA or 300mA?
Yes it would need to be time delayed... but looking at that, if both hager boards out of shot below the head are plastic, I'd just swap out that switch fuse for a new one and fit a 2pole 100ma type S / type A in there as that things got basic insulation hanging out it's arse anyway.
 
Yes it would need to be time delayed... but looking at that, if both hager boards out of shot below the head are plastic, I'd just swap out that switch fuse for a new one and fit a 2pole 100ma type S / type A in there as that things got basic insulation hanging out it's arse anyway.
I've got that and a lot lot more coded on the EICR 👍

I thought the tails needed to be protected regardless if the CU was plastic (they are)? Hence going to swap out the basic isolator and make that a 3P 100a 100mA time delayed RCD?

Or have I got that wrong?
 

Reply to Correct Type-S Upfront RCD for 3Ph TT System in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi, I was wondering if the wylex/Proteus SPD Isolators where dual isolator, they have 4 terminals at the bottom, can you use them to take 2 sets...
Replies
20
Views
3K
Hi all, First time post to the forums, I hope you all go easy on me! We are undertaking an electrical install as apart of a solar PV...
Replies
5
Views
966
I am going to need to install a small amount of galvanised steel conduit, leading down to perhaps 4 sockets and a light switch. This is in a...
Replies
38
Views
4K
I don't think I have worked with 32mm conduit before. Always 25mm and 20mm. I want to contain 2 x 25mm tails and 1 x 16mm earth in some 32mm...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock