Discuss Correct Type-S Upfront RCD for 3Ph TT System in the UK Electrical Forum area at ElectriciansForums.net

Oh sorry I misunderstood... so 3 phase head into what... 3x single phase switch fuses? Then off to each single phase board....
From this

IMG_3647.jpeg


Into the basic 100a 3pole Isolator
IMG_3660.jpeg


then from there round tothe 2 boards below the head and the third board has a fused switch at 60A

IMG_3650.jpeg
 
I am right is thinking it has to be a time delayed RCD upfront and not just a 100mA or 300mA?
Yes it would need to be time delayed... but looking at that, if both hager boards out of shot below the head are plastic, I'd just swap out that switch fuse for a new one and fit a 2pole 100ma type S / type A in there as that things got basic insulation hanging out it's arse anyway.
 
Yes it would need to be time delayed... but looking at that, if both hager boards out of shot below the head are plastic, I'd just swap out that switch fuse for a new one and fit a 2pole 100ma type S / type A in there as that things got basic insulation hanging out it's arse anyway.
I've got that and a lot lot more coded on the EICR 👍

I thought the tails needed to be protected regardless if the CU was plastic (they are)? Hence going to swap out the basic isolator and make that a 3P 100a 100mA time delayed RCD?

Or have I got that wrong?
 

Reply to Correct Type-S Upfront RCD for 3Ph TT System in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi, I was wondering if the wylex/Proteus SPD Isolators where dual isolator, they have 4 terminals at the bottom, can you use them to take 2 sets...
Replies
20
Views
3K
Hi all, First time post to the forums, I hope you all go easy on me! We are undertaking an electrical install as apart of a solar PV...
Replies
5
Views
982
I am going to need to install a small amount of galvanised steel conduit, leading down to perhaps 4 sockets and a light switch. This is in a...
Replies
38
Views
4K
I don't think I have worked with 32mm conduit before. Always 25mm and 20mm. I want to contain 2 x 25mm tails and 1 x 16mm earth in some 32mm...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock