Discuss TT Zs Readings and Tripping RCD? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

paulk11

Afternoon. Did a PIR on a TT installation yesterday with some confusing results.

Ze/RA was recorded as 116Ohms so as expected thereabouts. When Zs was tested it was found to be just 1.01 Ohms and 0.97 Ohms at a several points with just a few reading high as expected. As Zs = Ze+(R1+R2), it seems inconceivable that it can be that low. I',m thinking an alternative earth has sneaked in somewhere; (possibly a link to a TN system somewhere nearby?)

Following the Zs test, the RCD (S Type) started tripping and also failed the RCD test. We're now in a position where the RCD will stay made for a while but keeps tripping out for no apparent reason.

My initial thought is to change the RCD and see how that effects things.

Any suggestions?
 
Last edited:
your Zs readings are probably due to the extraneous water and gas supply pipes, which are a far better earth than a thin 3ft. stick in the ground. as for the RCD, no idea why. it could be faulty and having tripped once is now unstable. or you may have inadvertently introduced a fault on the installation if you have dismantled and reassembled sockets or otherwise.
 
The low Zs readings are more than likely a service bond.
It's not unheard of for a near by property to be tncs and the service pipe is acting as the conductor going back to the suppliers earth in the other property.

As for the RCD, it was probably stuck. And now you have tested it is tripping.
If it failed the test it needs replacing.
If your insulation resistance readings are ok and no faults present, then that would be a good place to start.
 
OK thanks a lot. There is no gas and the water bonding doesn't exist as it's a plastic incomer from the supply tap outside. The internal building domestic water system supplementary bonding is in place however, so I presume that's the only route the earth would have via the copper pipework. IR was all sound although was down to 125MegOhms - whole system tested in a single shot.

I'll get out and purchase a new one I think and give that a go for starters.

Cheers.
 
The RCD will hold for a while but then eventually trips for no obvious reason - it's not an instantaneous reaction on making the RCD switch.

One other thought, would the RCD be tripping if there was an imbalance of earths - i.e. a rod combined with a.n. other source? The RCD would respond to a difference in L-N?
 
The RCD will hold for a while but then eventually trips for no obvious reason - it's not an instantaneous reaction on making the RCD switch.

One other thought, would the RCD be tripping if there was an imbalance of earths - i.e. a rod combined with a.n. other source? The RCD would respond to a difference in L-N?

I think you need to read up on how RCD's work.

Is it a 30mA RCD or 100mA?
 
I think you need to read up on how RCD's work.

Is it a 30mA RCD or 100mA?

Thanks for that Murdoch; think I have it all clear - toroidal coils etc! Take the question more as seeking confirmation of a firm comprehension of the operation also, my text above confirms the reason why an RCD would trip.

30mA delayed

I did get some very useful info from fellow posters and having just replaced the RCD in question all seems good now with this particular RCD however it seems there may be a problem with another one so no wonder we were baffled by this inspection.
 
30mA delayed

I did get some very useful info from fellow posters and having just replaced the RCD in question all seems good now with this particular RCD however it seems there may be a problem with another one so no wonder we were baffled by this inspection.

??????
 
Set up is:
DB1: DP Iso switch with various circuits split between 2 30mA delayed RCDs so discrimination is achieved.
DB2: 30mA RCCB protecting 3 circuits.
Both DBs are supplied separately from mains supply.
 
Set up is:
DB1: DP Iso switch with various circuits split between 2 30mA delayed RCDs so discrimination is achieved.
DB2: 30mA RCCB protecting 3 circuits.
Both DBs are supplied separately from mains supply.

why the tine delay if they are final circuits?
 
It's what we found when we turned up to do the inspection so not planning to change things. I'll be recommending that the RCCB gets changed and all will be good........

Thanks for the advice - it threw us yesterday but hopefully sorted soon.
 
It's what we found when we turned up to do the inspection so not planning to change things. I'll be recommending that the RCCB gets changed and all will be good........

Thanks for the advice - it threw us yesterday but hopefully sorted soon.

this all sounds very odd.

could you post a picture of each CU? Not seen one with 2 x time delayed rcd's
 
The other thing is with a seized RCD is there could well be faults present but now the RCD has been released although faulty , would now mean that simply replacing it would also mean rectifying the faults too..
 
Only thing i could add to above,is, has leakage been clamped? and was test apparatus suitable for testing TD RCD?
 
Why would you put a time delayed 30 mA units in as they are not offering additional protection for anything as they will not disconnect in time to offer this or is there something special about this instal we need to know about.

I might be missing the obvious here as I am not that bright!
 
Didn't even know a 30mA time delayed RCD or RCBO existed.
 

Reply to TT Zs Readings and Tripping RCD? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock