Discuss TT Zs Readings and Tripping RCD? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

They do, but I have only ever known them be made to order by specialist protection companies. I can't imagine them ever being used in anything other than a specialist installation, they aren't exactly cheap!

Yes indeed. I've had a quick search and such beasts can be ordered but surely putting these into a domestic situation for final circuits would mean that the tripping times required of 300mS @ 30mA and 40mS @ 150mA are not met.
 
OK, all credibility (as if I ever had any anyway) is about to be ruined!

Having checked the info, they are standard RCDs and not time delayed!! I was going on colleagues info (honest) and not physically checked the details myself. So all advice above is much appreciated and fully understood. It's all a learning process :sick:

Cheers
 
Yes indeed. I've had a quick search and such beasts can be ordered but surely putting these into a domestic situation for final circuits would mean that the tripping times required of 300mS @ 30mA and 40mS @ 150mA are not met.

Yes exactly, they are no use for shock protection.
I think they see use as a backup fault protection when 10mA protection is used. But I could be wrong
 

Reply to TT Zs Readings and Tripping RCD? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock