Discuss Twin and earth testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

E

elektrisien

Hi,
A quick question, maybe a stupid one .... but it baffles me ,and I cannot find any info on the net. If you do the continuity test on a lighting circuit to get your resistance values, wired in twin and earth, how do you the the value for the earth ? Obviously you link the earth and phase or neutral, you get your reading ..... but the earth is of a smaller diameter, so the resistance is higher.... you cannot just divide it by two. So what is the secret ? Let me just say, I am just starting to do testing, so excuse my ignorance ..
 
if you want the resistance of the cpc ( earth) on it's own, then you need to use a wander lead. either null your tester with wander lead on it's own, or subtract it's resistance from the reading.
 
Most test sheets require either R1+R2 or R2.

You could calculate it from R1+R2 as Murdoch says, but this could be incorrectly influenced by an circuit fault such as a high resistance joint on the line conductor which would increase the value of R1+R2 but wouldn't cause any increase to R2 on it's own.
 
if you want the resistance of the cpc ( earth) on it's own, then you need to use a wander lead. either null your tester with wander lead on it's own, or subtract it's resistance from the reading.

If you didn't have the wander lead, might you measure R1 + Rn and take half of this value away from R1 + R2, leaving you with a reasonably accurate value of R2. That said ... the neutrals do not always follow the entire route of the line and switched line circuit so scratch that one!
 

Reply to Twin and earth testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
618
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
812
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
859
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
427

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock