Search the forum,

Discuss Twin immersion same circuit? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I've purchased a horizontal unvented cylinder that has come with 2 immersion heaters.

I was hoping to use the same circuit the my existing tank used.

What's the best way to wire in for 2 immersions? Upgrade the 2.5mm radial?

Any suggestions welcome
 
If you only have one (presumably) 16A circuit, you can get a controller that connect two elements, but only allows one to be switched on at any one time. Typically used so the main lower element is put on at an off-peak time (over night) and the higher boost element when you need to top up the heat in the tank.

Edit: Or is this a large tank designed to use both elements together?
 
I've purchased a horizontal unvented cylinder that has come with 2 immersion heaters.

I was hoping to use the same circuit the my existing tank used.

What's the best way to wire in for 2 immersions? Upgrade the 2.5mm radial?

Any suggestions welcome
Do you have a two tariff supply ?

You could use a Bath / Sink mode switch using your existing wiring.

It may be beneficial to install two circuits if you have a peak and off-peak consumer unit.
 
Do you have a two tariff supply ?

You could use a Bath / Sink mode switch using your existing wiring.

It may be beneficial to install two circuits if you have a peak and off-peak consumer unit.
No just a single tariff. The tank is 250l horizontal which is why I guess they supply with two immersion.
 
One would do the job but if your planning on using both at the same time you'll have to either upgrade the cable and protective device or run a new circuit for the second immersion.
 
No just a single tariff. The tank is 250l horizontal which is why I guess they supply with two immersion.
They should never really be run together, the intention of having 2 elements is that the top element keeps the top part of the tank hot for use when you aren't needing lots of hot water.

The easiest way is to fit a bath/sink switch or as already said a controller.
 
They should never really be run together, the intention of having 2 elements is that the top element keeps the top part of the tank hot for use when you aren't needing lots of hot water.

The easiest way is to fit a bath/sink switch or as already said a controller.
I'm a bit confused here...There is no top or bottom?? It's a horizontal tank and they're both at the same level
 
I'm a bit confused here...There is no top or bottom?? It's a horizontal tank and they're both at the same level
Ahh different type to what i had in my head, so your one is not economy 7 type but a dual element which will heat the whole tank whichever element is used but will obviously do it quicker.




Untitled.jpg


Unless you want faster heating of the tank, then just leave it on the one element, otherwise you will have to run a new circuit to run both at the same time.
 
Last edited:
Seen plenty of horizontal cylinders for electric wet CH systems but never indirect cylinders, just took a look they are quite big holds quite a few litres of water.
 
Seen plenty of horizontal cylinders for electric wet CH systems but never indirect cylinders, just took a look they are quite big holds quite a few litres of water.
It's full weight is 300kg, Ive had a structural engineer draw up the plans for a platform in the loft. Wouldn't want to put that kind of weight on my ceiling joists. Guess it would be ok if I had a support wall underneath but I haven't.

Thanks for the suggestions, looks like beefing up the cable is the best option at the moment.
 
Where did you buy it from?

Won’t they have suggestions of how it should be connected up
Got it from Screwfix. A g3 plumber will be connecting it up.
As it won't be a straight swap for the immersion looks like I'll be getting an electrician in. I wanted to check with the professionals on here what options were available.

Just wondering if I could have another consumer consumer unit linked off the main one just for boiler/pump immersion 1 and immersion 2??
 
Got it from Screwfix. A g3 plumber will be connecting it up.
As it won't be a straight swap for the immersion looks like I'll be getting an electrician in. I wanted to check with the professionals on here what options were available.

Just wondering if I could have another consumer consumer unit linked off the main one just for boiler/pump immersion 1 and immersion 2??
Yes you could.

Can you give the model of tank you have ?
 
Yes you could.

Can you give the model of tank you have ?
Yes it's a Prostel indirect 250l horizontal. It's an RM cylinder so came delivered from Joule.

It's in Screwfix. The pic you see in Screwfix is not the right one as it shows just one immersion at the top entry but mine has two immersion along the side.
 

Reply to Twin immersion same circuit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
695
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
488
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
239

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock