Discuss Two 16amp ovens on 32amp mcb B supply in the DIY Electrical Advice area at ElectriciansForums.net

andypo

DIY
Reaction score
0
Hi,

I am replacing an old double oven with 2 new small ovens. The old oven is wired into a dedicated supply with a switch and the consumer board has a 32amp MCB B breaker.

New oven 1 requires a 15 amp fuse and 2790W. link below.

New oven 2 requires a 16 amp fuse and 2790W. link below.

Can the existing 32amp MCB B supply be repurposed for the 2 new ovens by connecting a 42amp dual connection plate to the existing switch?

Thanks.
 
If the manufacturer recommends 15/16A fuses, I would either (a) downgrade the protective device of the existing circuit and use that, along with install a new circuit for the other or (b) put a small consumer unit like one of the BG garage units on the end of the existing cable and put two 16A breakers/RCBOs in there and supply both from that.

Whilst we can all agree that running a 2.5mm to each device (given we can do that when spurring off a ring) to the ovens will probably not be a problem, if the manufacturers state it should be on a 16A fuse, it's unlikely we could come up with justification for now following their guidance and as such if anything does go bad internally at the very least they have a get out when it comes to honouring warranty terms and if it goes really bad you're on the hook rather than them as you've ignored their guidance.
 
If the manufacturer recommends 15/16A fuses, I would either (a) downgrade the protective device of the existing circuit and use that, along with install a new circuit for the other or (b) put a small consumer unit like one of the BG garage units on the end of the existing cable and put two 16A breakers/RCBOs in there and supply both from that.

Whilst we can all agree that running a 2.5mm to each device (given we can do that when spurring off a ring) to the ovens will probably not be a problem, if the manufacturers state it should be on a 16A fuse, it's unlikely we could come up with justification for now following their guidance and as such if anything does go bad internally at the very least they have a get out when it comes to honouring warranty terms and if it goes really bad you're on the hook rather than them as you've ignored their guidance.
Thanks! I'll go with the BG garage unit on the end of the existing supply. That's my weekend sorted :)
 
Thanks! I'll go with the BG garage unit on the end of the existing supply. That's my weekend sorted :)

Just be mindful that technically, you'll be adding a new consumer unit and two new circuits which makes this notifiable works under the building regulations (Approved Document P - You can search for this on-line, 2013 edition is the one that applies to England). As such you should either go through the planning process or employ the services of a member of one of the competent persons schemes who can notify the works on your behalf.

The BG Garage units you can buy off the shelf will typically include an RCD as the main switch along with a 32A and 6A circuit breaker. Depending on whats in the board supplying the existing supply, you may not need the RCD (it's not ideal having two RCDs in series) and the DIY sheds don't stock the board with a main switch.

If you'd like some indication of pricing, drop me a private message and I'll give you and idea of what I'd charge for this (including the building control notification, full documentation for the changes and the associated testing).
 

Reply to Two 16amp ovens on 32amp mcb B supply in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how my oven is currently wired up, followed by 3...
Replies
0
Views
934
D
Hi, I've searched these forums and have found quite a bit of good information, but not specifically to my query. My house is about 9 years old...
Replies
2
Views
2K
(Trying again, as picture didn't post first time) Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how...
Replies
5
Views
1K
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K
Hello. I have a new oven. I understand completely that I need to get it installed by an electrician and will definitely do so but for my own...
Replies
6
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock