Currently reading:
Two new Wylex RCDs both failed tests

Discuss Two new Wylex RCDs both failed tests in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
24
Folks,

A bit baffled (not difficult) ... added a light switch in a rental this week (empty property so no social distancing issues) and checked the RCD before I signed off. It was a Wylex 80a 30mA and it failed all tests (inc. ramp) so I like-for-like replaced it. The new one also failed all tests (1/2, 1, 5 and ramp). Figuring I'd got a faulty one I replaced it again with the same results.

So ... surely not 2 new dodgy Wylex RCDs? Must be a problem within the installation? Tried testing the RCD on its own with no loads, same result. RCD stays on and the manual test trip works.

Megger MFT1552, 30mA range, Ze 0.29ohms, PFC 0.78kA.

Do I need to go to dead tests?
 
suspect a N-E fault on the installation. can do weird things to RCDS, does the RCD test button work?
 
Your test meter could be faulty.Maybe it doesn't like Wylex RCD's? Try it on a different make? You also need to be checking the RCD completely on it's own.ie take out the live and neutral terminals at the bottom of the RCD so it's completely stand alone and then try testing it again.If it now works then ,like others have said, it's probably a neutral fault.
 
Your test meter could be faulty.Maybe it doesn't like Wylex RCD's? Try it on a different make?

I did wonder. I've tested Wylex before and not had a problem. I also changed the batteries in case they were going bad. I'll check my RCDs here at home just to be sure though. Thanks
[automerge]1585507205[/automerge]
.... take out the live and neutral terminals at the bottom of the RCD so it's completely stand alone and then try testing it again.If it now works then ,like others have said, it's probably a neutral fault.

Aha, yes, makes sense to isolate the issue a bit more. I'll do that too.
 
Last edited:
OK, thought I'd update you all on this one.

Yes indeed, there was a fault between N and E. I isolated the RCD which then tested fine. I then disconnected the earth(s) for the lighting circuit - the first circuit I checked - and the RCD then tested fine. I reconnected each of the 4 (!) lighting radials one at a time and found the fault on the downstairs lights.

I'm currently looking for where exactly the fault is but it's certainly not in a light or a switch as I checked those already. Screw through a cable likely ...

Thanks for the help here guys.
 
Depends on whether the neutral/earth fault causes an imbalance. Just because you have a neutral/earth fault it should not be assumed the circuit will follow the earth path, circuit impedance may dictate the circuit carries on down the neutral path hence no imbalance.
 
The behaviour of an N-E fault is complex and can seem unpredictable. There are paths of different resistances to both neutral and earth for current from the faulty circuit, from other circuits and even from neutrals of other installations when there's no load on this one. How each of the currents divides can be hard to predict; sometimes they will cause nuisance tripping when there is heavy load on, sometimes just failure to test, sometimes the RCD won't reset at all.

What they should do consistently, though, is fail insulation tests, so I am a little surprised that wasn't picked up first.
 

Reply to Two new Wylex RCDs both failed tests in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top